Per the data sheets, you don't need to sprig on 3" pipe
Individual pipes and conduit 4 inches (102 mm) diameter or less 3-inch
(DN80) pipe size or less will not require sprigs).
On 11/29/2011 7:30 AM, Steve Mackinnon wrote:
I haven't used them either, but I did do some light reading on the topic
recently;
Cons: must be raised (sprig's or candle sticks) above piping 3" and
larger
Pro: eliminate some obstruction rules vs pendent ESFR heads
Customer gains more storage room (sprinkler head in upright
position vs pendent)
Just a few comments...
Steven
Steven MacKinnon
Senior Fire Protection Engineer
Hartcorn Plumbing& Heating Inc.
850 South 2nd Street
Ronkonkoma, NY 11779
631-580-2300 - Office
631-580-1090 - Fax
[email protected]
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Cesar
Lira
Sent: Saturday, November 26, 2011 12:00 PM
To: [email protected]
Subject: Up-Right ESFR K17 AH
I Found an Up-Right ESFR K17 Tyco,. but..
Does anyone know when can I use It?,.. if the proper branch line could
be an
obstruction.
Normally or never I have used an Esfr Up-right.
Cesar L.
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20111126/0627770d/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum