Now that FM allows 60ksf, I have had more success convincing AHJ's that 
sprinkler systems still work when they exceed 52K.

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd - FPDC
Sent: Monday, January 02, 2012 12:46 PM
To: [email protected]
Subject: Re: 52,000 square feet

Chris, I agree is that is what the Code says. However, the 52000 is an 
arbitrary number and has no real impact on protection. For a couple of thousand 
square feet, I wouldn't have a big problem suggesting it. Probably 3k max. 

Sent from my iPhone

On Jan 2, 2012, at 12:46 PM, "Cahill, Christopher" <[email protected]> wrote:

> As a former AHJ many requests, all denied with I agree it's silly but it's 
> the law.  
> 
> As a former contractor wanted to make such requests but never did because 
> it's not compliant with the law.
> 
> As a current consultant would only make such request if specifically 
> instructed by the client over my clearly documented objections. (with the 
> hope the AHJ would back the law)
> 
> And I don't think one can put a 52,000 sq.ft. aux dry system off a 52,000 
> sq.ft. wet system as an example.  The combined systems are still limited to 
> 52,000 sq.ft.  So adding a control valve and flow switch at the additions off 
> the existing isn't going to help.
> 
> As any role would suggest if you can easier cut off 6,000 sq.ft. near the 
> riser and turn that into its own system.  Avoids the long run and then add 
> the new 6,000 to the end.  
> 
> Chris Cahill, PE*
> Senior Fire Protection Engineer
> Aviation & Facilities Group
> Burns & McDonnell
> P:  952.656.3652
> F:  952.229.2923
> [email protected]
> www.burnsmcd.com
> *Lic. in MN
> 
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Bob
> Sent: Monday, January 02, 2012 11:31 AM
> To: [email protected]
> Subject: RE: 52,000 square feet
> 
> Greg,
> I think that option two would be ok.  It seems that it's ok to have an 
> auxiliary dry system off the end of a wet system, so an auxiliary wet system 
> should work as well.
> 
> 
> 
> Bob Knight, CET III
> 208-318-3057
> www.firebyknight.com
> 
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Greg McGahan
> Sent: Monday, January 02, 2012 10:04 AM
> To: [email protected]
> Subject: 52,000 square feet
> 
> We have a school that is getting 2 small additions at the end of the wings of 
> approx. 6,000 and 3,000 sqft respectively. If we tried to tie on to the end 
> of one system to feed the larger addition, that system would be approximately 
> 56,000 sqft. Th other two options (I guess) would be to run 250' of 3" back 
> to the main riser and create a new system for this addition, or use it for 
> both additions with another 300' or so of main, or maybe to put in a new 
> control valve and flow switch at each addition to supply them.
> I am not sure if the second option would meet the intent of the code and I am 
> too confused to figure this out this early in the year.
> 
> The other addition appears to be on a system that is already about 53,000 
> sqft and adding the addition would also put it around the 56,000 mark.
> 
> Has anybody ever asked for a variance on something like this? It honestly 
> doesn't make any sense to put it in a separate system (other than to meet
> code) because the operation of the system will not actually be effected.
> Especially in the way these systems are shaped, there are several different 
> fire rated zones of much smaller area.
> 
> Happy New Year and thanks,
> 
> --
> Greg McGahan
> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> fax 850-937-1852
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
> s/20120102/1eb1176e/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> -----
> No virus found in this message.
> Checked by AVG - www.avg.com
> Version: 2012.0.1901 / Virus Database: 2109/4718 - Release Date: 01/02/12
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to