It would be great if there were allowances for  systems that could be
subdivided so that no more than xxx sq ft is disabled at a time rather than
limit the entire system size.

On Tue, Jan 3, 2012 at 9:38 AM, Cahill, Christopher <[email protected]>wrote:

> I'm not sure I agree they need to go away.  I understand they didn't
> exactly come from a well thought out principal based on some scientific
> merit.  But my reasoning goes like this.  In a 208,000 sq.ft. building
> right now we would have 4 systems.  If a system is down for maintenance or
> say to add a head in a new office there is a 75% chance the fire will start
> in a sprinklered area.  And yes I have been involved with two buildings
> where the system was off when the fire started.  Get rid of the limits and
> there is a 100% chance the fire starts in an unsprinklered area during
> these same down times.  Double the current limits and it's 50/50.
> Remember most work is in design build which almost always = lowest bid =
> one system per building.
>
> Sure make the argument some places will have thoughtful engineers,
> thoughtful contractors, or owners that are interested in issues like this
> and I won't argue but what about the majority of work.  Modify the limits
> perhaps but they shouldn't go away.  Maybe something like warehouses 100k,
> HPS 40k, single tenant office buildings 50k, lease office 30k, malls by
> tenant.  By floor in lease or malls, building over 4 stories.
>
> Chris Cahill, PE*
> Senior Fire Protection Engineer
> Aviation & Facilities Group
> Burns & McDonnell
> P:  952.656.3652
> F:  952.229.2923
> [email protected]
> www.burnsmcd.com
> *Lic. in MN
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Ron Greenman
> Sent: Tuesday, January 03, 2012 9:16 AM
> To: [email protected]
> Subject: Re: 52,000 square feet
>
> These limitations need to go away. They're based on pipe schedules, and
> not because the limitations are true , but merely because the schedule
> stops at
> 400 heads. In the days when schedules were developed 52K was a really big
> building.
>
> On Mon, Jan 2, 2012 at 10:48 AM, Matt Grise <[email protected]> wrote:
>
> > Now that FM allows 60ksf, I have had more success convincing AHJ's
> > that sprinkler systems still work when they exceed 52K.
> >
> > Matt Grisé PE*, LEED AP
> > Sales Engineer
> > Alliance Fire Protection
> > 130 w 9th Ave.
> > North Kansas City, MO 64116
> >
> > *Licensed in KS & MO
> >
> > 913.888.0647 ph
> > 913.888.0618 f
> > 913.927.0222 cell
> > www. AFPsprink.com
> >
> > -----Original Message-----
> > From: [email protected] [mailto:
> > [email protected]] On Behalf Of Todd - FPDC
> > Sent: Monday, January 02, 2012 12:46 PM
> > To: [email protected]
> > Subject: Re: 52,000 square feet
> >
> > Chris, I agree is that is what the Code says. However, the 52000 is an
> > arbitrary number and has no real impact on protection. For a couple of
> > thousand square feet, I wouldn't have a big problem suggesting it.
> > Probably 3k max.
> >
> > Sent from my iPhone
> >
> > On Jan 2, 2012, at 12:46 PM, "Cahill, Christopher"
> > <[email protected]>
> > wrote:
> >
> > > As a former AHJ many requests, all denied with I agree it's silly
> > > but
> > it's the law.
> > >
> > > As a former contractor wanted to make such requests but never did
> > because it's not compliant with the law.
> > >
> > > As a current consultant would only make such request if specifically
> > instructed by the client over my clearly documented objections. (with
> > the hope the AHJ would back the law)
> > >
> > > And I don't think one can put a 52,000 sq.ft. aux dry system off a
> > 52,000 sq.ft. wet system as an example.  The combined systems are
> > still limited to 52,000 sq.ft.  So adding a control valve and flow
> > switch at the additions off the existing isn't going to help.
> > >
> > > As any role would suggest if you can easier cut off 6,000 sq.ft.
> > > near
> > the riser and turn that into its own system.  Avoids the long run and
> > then add the new 6,000 to the end.
> > >
> > > Chris Cahill, PE*
> > > Senior Fire Protection Engineer
> > > Aviation & Facilities Group
> > > Burns & McDonnell
> > > P:  952.656.3652
> > > F:  952.229.2923
> > > [email protected]
> > > www.burnsmcd.com
> > > *Lic. in MN
> > >
> > >
> > > -----Original Message-----
> > > From: [email protected] [mailto:
> > [email protected]] On Behalf Of Bob
> > > Sent: Monday, January 02, 2012 11:31 AM
> > > To: [email protected]
> > > Subject: RE: 52,000 square feet
> > >
> > > Greg,
> > > I think that option two would be ok.  It seems that it's ok to have
> > > an
> > auxiliary dry system off the end of a wet system, so an auxiliary wet
> > system should work as well.
> > >
> > >
> > >
> > > Bob Knight, CET III
> > > 208-318-3057
> > > www.firebyknight.com
> > >
> > >
> > >
> > > -----Original Message-----
> > > From: [email protected]
> > > [mailto:[email protected]] On Behalf Of Greg
> > McGahan
> > > Sent: Monday, January 02, 2012 10:04 AM
> > > To: [email protected]
> > > Subject: 52,000 square feet
> > >
> > > We have a school that is getting 2 small additions at the end of the
> > wings of approx. 6,000 and 3,000 sqft respectively. If we tried to tie
> > on to the end of one system to feed the larger addition, that system
> > would be approximately 56,000 sqft. Th other two options (I guess)
> > would be to run 250' of 3" back to the main riser and create a new
> > system for this addition, or use it for both additions with another
> > 300' or so of main, or maybe to put in a new control valve and flow
> > switch at each addition to supply them.
> > > I am not sure if the second option would meet the intent of the code
> > > and
> > I am too confused to figure this out this early in the year.
> > >
> > > The other addition appears to be on a system that is already about
> > 53,000 sqft and adding the addition would also put it around the
> > 56,000 mark.
> > >
> > > Has anybody ever asked for a variance on something like this? It
> > honestly doesn't make any sense to put it in a separate system (other
> > than to meet
> > > code) because the operation of the system will not actually be
> effected.
> > > Especially in the way these systems are shaped, there are several
> > different fire rated zones of much smaller area.
> > >
> > > Happy New Year and thanks,
> > >
> > > --
> > > Greg McGahan
> > > Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> > > 1160 McKenzie Road
> > > Cantonment, FL 32533
> > > 850-937-1850
> > > fax 850-937-1852
> > > -------------- next part -------------- An HTML attachment was
> > > scrubbed...
> > > URL:
> > > <
> > http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attac
> > hment
> > > s/20120102/1eb1176e/attachment.html>
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > > -----
> > > No virus found in this message.
> > > Checked by AVG - www.avg.com
> > > Version: 2012.0.1901 / Virus Database: 2109/4718 - Release Date:
> > > 01/02/12
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC
>
> They are happy men whose natures sort with their vocations. -Francis
> Bacon, essayist, philosopher, and statesman (1561-1626)
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120103/c5838ccd/attachment.html
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120103/0d9a9834/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to