We have been putting on either a exposed 3-way FDC when 750gpm is required or 
2- 2 1/2" x 2 1/2" x 4" dual clapper FDC's then 1000gpm is required.
Dewayne

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Wednesday, February 01, 2012 8:58 AM
To: [email protected]
Subject: Standpipe FDC Inlets

How many of you put a 4 way FDC on every 1000 gpm standpipe system or a 5 way 
on parking garage without sprinklers and 4 or more standpipes? I have seen many 
buildings with two standpipes and a 2 way FDC.

2007, NFPA 14, 7.12.3 states: Fire Department Connection sizes shall be based 
on the standpipe system demand and shall include one 2½ in. inlet per every 250 
GPM.

Phoenix at one time required one inlet per 250 gpm on sprinkler systems until 
we did a tire warehouse and needed a 14 inlet FDC.

Ron Fletcher
Aero Automatic
Phoenix, AZ