Hold on there Todd. An FDC can be approved - see 6.8.1.1 and other references in both 13 and 14. If the serving FD wants an FDC configured a certain way because that's how they're equipped and programmed for firefighting operations, then by all means give the EXACTLY WHAT THEY WANT. It's their connection ...
SML -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Todd Williams Sent: Wednesday, February 01, 2012 8:45 AM To: [email protected] Subject: RE: Standpipe FDC Inlets At 11:28 AM 2/1/2012, you wrote: >Now, what has the forum done when the AHJ requires a 5"X4" storz >connection instead? We have only been putting one for standpipes >1000gpm and under. >Dewayne I tell them that since they are not UL listed for fire service, they are not legal in the State of Connecticut (per State Fire Marshal) Todd G. Williams, PE Fire Protection Design/Consulting Stonington, CT 860.535.2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum