Hold on there Todd.   An FDC can be approved - see 6.8.1.1 and other
references in both 13 and 14.   If the serving FD wants an FDC
configured a certain way because that's how they're equipped and
programmed for firefighting operations, then by all means give the
EXACTLY WHAT THEY WANT.  It's their connection ...

SML




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd
Williams
Sent: Wednesday, February 01, 2012 8:45 AM
To: [email protected]
Subject: RE: Standpipe FDC Inlets

At 11:28 AM 2/1/2012, you wrote:
>Now, what has the forum done when the AHJ requires  a 5"X4" storz
>connection instead?  We have only been putting one for standpipes
>1000gpm and under.
>Dewayne


I tell them that since they are not UL listed for fire service, they are
not legal in the State of Connecticut (per State Fire Marshal)




Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com