Rick Santorum says yes, Mitt Romney says no, they both say Barack Obama
is ruining the American way of life with elevator hoistway sprinklers.

Sorry, I digressed.

Actually, shaft provisions in NFPA 13 are mute with regard to valving -
that really goes back to local authorities.  Here in CA, there is a an
elevator division of CAL-OSHA that has jurisdiction over all hoistways
and equipment rooms.   Their rules supersede provisions of all building
and fire codes and referenced standards. It is not uncommon for
sprinklers to impact the configuration of alarm systems and to trigger
interface with shunt/trip breaker requirements for elevator power.
Putting a sprinkler at the top, if it's not a combustible shaft, isn't a
common practice anymore, but valving for shut-off is.  My guess is that
the specific answer to your question lies with the Michigan state
elevator AHJ, or the local if there is no such state agency.

Steve Leyton




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Wednesday, February 22, 2012 12:42 PM
To: SprinklerFORUM
Subject: Elevators - Michigan rules

I am designing a job in Michigan that will require sprinklers at the top
/ bottom of the elevator shaft and the equipment room.

Do these need to be provided with a shutoff valve/s?  

Thanks,

 

Dewayne Martinez

Design Build Fire Protection

262-784-7900 (w)

262-784-8401 (f)

414-349-0468 (cell)

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120222/9ef83497/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to