Some AHJ's require that we use a parallel line for the reduced water supply so 
the residual would be reduced the same as the static, in this case 25 psi. The 
flow remains the same. Depending on the pressure decrease the graph could 
actually indicate a negative residual pressure at flow so a percentage 
reduction makes more sense. If the static reduction is 33% then I would reduce 
the residual 33%.

Ron Fletcher
Aero Automatic
Phoenix, AZ



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Mackinnon
Sent: Thursday, February 23, 2012 6:58 AM
To: [email protected]
Subject: Historical lows on Water Flow tests

I have a question about the "Historical low" noted on Water Flow Tests from 
Government agencies (i.e. County, Town, City Water companies). 
Recently I received a test with the results; Static - 75 psi Residual - 54 psi 
Flow - 671 gpm.

At the top of the letter they through in, "Historically, the static pressure in 
this area has been as low as 50 psi." So a 25 psi drop in static pressure. 

My question is, how do you adjust the residual pressure and flow?
Normally I would lower the residual the same pressure drop as the static. With 
the above example, I would have a residual of 29 psi with a flow of 671 gpm.

Should the flow change too??

Has anyone else experienced a similar situation?

Thank you in advance for any guidance.

Steven



Steven MacKinnon
Senior Fire Protection Engineer
Hartcorn Plumbing & Heating Inc.
850 South 2nd Street
Ronkonkoma, NY 11779
631-580-2300 - Office
631-580-1090 - Fax
[email protected]
 
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to