NFPA 13 2007 8.15.15.3 allows old style sprinklers "where construction features 
or other special conditions require unique water distribution."

Has anyone come across such a situation?

For example:
I have a building where there is some structural steel passing through a 
non-combustible, non-accessible, mechanical shaft (that was previously 
un-sprinklered). For whatever reason, they feel like it will be extremely 
difficult to get fire-proofing onto the steel, so the architect suggested using 
old-style sprinklers to protect the roof structure and steel below (since they 
spray up and down). It was my understanding that standard spray sprinklers are 
used now specifically because they work better at protecting the structure 
above them (and better at attacking the fire), but I wanted to double check. 
Any thoughts?

Thanks!