I'm not sure if they still make old style sprinkelrs

At 09:17 AM 2/29/2012, you wrote:
>NFPA 13 2007 8.15.15.3 allows old style sprinklers "where construction 
>features or other special conditions require unique water distribution."
>
>Has anyone come across such a situation?
>
>For example:
>I have a building where there is some structural steel passing through a 
>non-combustible, non-accessible, mechanical shaft (that was previously 
>un-sprinklered). For whatever reason, they feel like it will be extremely 
>difficult to get fire-proofing onto the steel, so the architect suggested 
>using old-style sprinklers to protect the roof structure and steel below 
>(since they spray up and down). It was my understanding that standard spray 
>sprinklers are used now specifically because they work better at protecting 
>the structure above them (and better at attacking the fire), but I wanted to 
>double check. Any thoughts?
>
>Thanks!
>
>Matt Grisé PE*, LEED AP
>Sales Engineer
>Alliance Fire Protection
>130 w 9th Ave.
>North Kansas City, MO 64116
>
>*Licensed in KS & MO
>
>913.888.0647 ph
>913.888.0618 f
>913.927.0222 cell
>www. AFPsprink.com
>
>-------------- next part --------------
>An HTML attachment was scrubbed...
>URL: 
><http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120229/0a96807c/attachment.html>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to