The IBC has fire sprinkler requirements in it for H buildings that exceed
the requirements of NFPA (similar to dry heads on a deck in a 13R scenario),
they are hard to find in that book, but they are there, not to mention
containment issues an H building requires for sprinkler systems in an H
occupancy.
Bill Cunningham
Plumbco Inc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Thursday, March 01, 2012 11:15 AM
To: [email protected]
Subject: RE: Fiberglass Fabrication Shop

"H" is not related to the sprinkler system design.  That's a possible
building code occupancy classification.

I did one of these years ago for a major bathroom fixture mfgr.  There are
multiple hazards which can be present, all of which may need to be dealt
with differently.

So just to say you have a "fiberglass fabrication shop" doesn't provide
enough info.

We had resin spray booths, materials storage including flammable liquids,
finished product storage (racks), grinding and finishing (lots of dust),
pallet storage, just as an overview.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of å... ....
Sent: Thursday, March 01, 2012 2:09 PM
To: [email protected]
Subject: Fiberglass Fabrication Shop

depending on the quantity and type of hardeners
(e.g. epoxies) you may have a H-area.


Scot Deal
Excelsior Fire Engineering
FPE/PE USA






On Thu, Mar 1, 2012 at 8:51 AM, Cory Power
<[email protected]>wrote:

> We were asked to quote a 4100 sq.ft fiberglass fabrication shop. What
> hazard would this be considered as? All I can find in nfpa 13 that could
be
> applicable is "resin application area" which says Ordinary Hazard Group 2.
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <http://fireball.**firesprinkler.org/mailman/**
>
private/sprinklerforum/**attachments/20120301/22273b96/**attachment.html<htt
p://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20
120301/22273b96/attachment.html>
> >
> ______________________________**_________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.**org <[email protected]>
>
http://fireball.firesprinkler.**org/mailman/listinfo/**sprinklerforum<http:/
/fireball.firesprinkler.org/mailman/listinfo/sprinklerforum>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120301/682027a1/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to