My thinking is because they go right to the face of the rack and the tires
below are only protected by what trickles through on single racks and by
what trickles through and enters the flue space on the double row racks -
you do not get complete coverage to this level of tires

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax 
(731) 267-4853 cell
www.keyfireprotection.com
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Monday, March 12, 2012 1:32 PM
To: [email protected]
Subject: RE: Tire Storage

Why does the bottom 8 ft of storage have to be protected twice? If the
ESFR's at the roof can do the storage the sprinklers below the grating are
to protect the aisle and OH2 should be adequate.

Ron Fletcher
Aero Automatic
Phoenix, AZ



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Monday, March 12, 2012 11:00 AM
To: [email protected]
Subject: RE: Tire Storage

Roland,

I felt like if the ceiling is designed based on the 16'-0 high rack scenario
and this will cover to the floor in the areas where the mezzanine is open
(between racks in front of some, etc.). Then under the mezzanine protect
this based on the same storage scenario but for 8'-0 high tire storage with
water shields on the sprinklers; whether it be ESFR, Large Drop, Control
Mode Density Area, etc. as long as it is per Chapter 18 then it would be
fine.

I guess this statement is false now?

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
www.keyfireprotection.com
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Monday, March 12, 2012 12:35 PM
To: [email protected]
Subject: Re: Tire Storage

This issue was tangentially discussed by the TC this cycle.  It was  
flagged by several of us that explicit guidance is needed for ceilings  
that are metal grating such as mezzanines.  It would also apply to  
walkways as discussed here.  Nonetheless, the TC statement does shed  
some light on addressing it (see below). To set the stage, the  
submitted comment was for a single design criteria for all situations.

Roland

ROC 13-257
Committee Meeting Action: Reject
Committee Statement: A single design basis does not adequately address  
the different conditions that can exist beneath all locations using  
grating. Sprinklers
beneath gratings that are obstructions should mimic the ceiling design  
basis and when beneath a floor can be a separate design basis.

On Mar 12, 2012, at 9:52 AM, Bobby Gillett wrote:

> Agree, that is what I was thinking  - any suggestions on the lower  
> level?
> Just base it in what it is - 8'-0 high rack storage for tires on  
> tread in
> fixed open racks?
>
> Bobby Gillett
> Sr. Project Manager

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120312/bb2c1071/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.1913 / Virus Database: 2114/4866 - Release Date: 03/12/12

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2012.0.1913 / Virus Database: 2114/4866 - Release Date: 03/12/12

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to