Their concern is with the fuel lines between the pump and the tank.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of [email protected]
Sent: Tuesday, March 13, 2012 11:54 AM
To: [email protected]
Subject: Re: Control of diesel fuel spillage in pump house

We have had that issue.  Same situation - standalone pump house with
diesel-driven pumps.  It depends on how paranoid the local environmental
authority is.   The pump house was originally a diked floor but the
foundation settled so now there are cracks in the floor.  We had to dike
the fuel tanks and then were ordered to install a curtain around the tanks.
Think shower curtain to contain a leak in case the tank sprung a leak and
shot past the diking.   Then, they wanted a dike around the fire pumps.  So
at the base of each pump we had to construct a sheet metal dike at the edge
of the pad.  The only thing not covered was the fuel line between the tanks
and the pumps but it was a solid line with no fittings.  He was concerned
about leaks at the fittings.  At least we didn't have to shower curtain the
pumps.  Ssh.  That might be next.  The shower curtain is a royal pain in
the kiester.  Obstructs vision of the gage glass and just generally gets in
the way.   It seems overkill for the frequency of the type of event they
are paranoid about.


John Hoffman P.E. | Fire Protection Engineer | Facility Engineering
Services, KCP, LLC - Burns & McDonnell Engineering | National Nuclear
Security Administration's Kansas City Plant | Operated by Honeywell FM&T |
2000 E. 95th St | Kansas City, MO  64131 | ph 816-997-7213 |
[email protected]



From:   <[email protected]>
To:     <[email protected]>
Date:   03/13/2012 10:22 AM
Subject:        Control of diesel fuel spillage in pump house
Sent by:        [email protected]



I've got a corporate Emergency and Health manager asking the question about
what happens to the diesel fuel if a pipe is broken within a diesel pump
house, where does it go or how is it contained?  Never had anyone ask this
question before. Tank is double wall, not an issue.

Background: The diesel pump is located in a standalone manufactured fire
pump house (package deal, all assembled in the factory), 1500 gpm pump set.
Industrial site setting.

There is a low level alarm on the fuel tank but if you were relying on that
to signal a leak it would be too late by the time the signal alarmed.
There is a 2" floor drain in the pump house but their concern is whether
the diesel would run to the drain and into the municipal sanitary sewer
system.  Definitely a no-no.

Anyone else had this question raised by an AHJ or risk consultant?

Craig L. Prahl, CET
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to