That's what I thought but just wanted to check with the forum. If I remember correctly from past forum postings, I would not have to apply it to the res sprinklers either because they are not calculated using the area-density method. That is unless we are applying 13 (10ed).
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Matt Grise Sent: Thursday, March 15, 2012 8:56 AM To: [email protected] Subject: RE: CC2/ RESIDENTIAL - AREA INCREASE I am not sure if that would apply since CC2 heads have an operating area dictated by their listing. Matt Grisé PE*, LEED AP, NICET II Sales Engineer Alliance Fire Protection 130 w 9th Ave. North Kansas City, MO 64116 *Licensed in KS & MO 913.888.0647 ph 913.888.0618 f 913.927.0222 cell www. AFPsprink.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Dewayne Martinez Sent: Thursday, March 15, 2012 7:44 AM To: SprinklerFORUM Subject: CC2/ RESIDENTIAL - AREA INCREASE NFPA 13 (02ed) section 11.2.3.1.8 (3) Does the 3000 SF area increase of this section apply to CC2 and residential sprinklers? I know NFPA 13 2010 provides some guidance but this AHJ follows 2002. Thanks, Dewayne Martinez Design Build Fire Protection 262-784-7900 (w) 262-784-8401 (f) 414-349-0468 (cell) -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120315/b91ccfc6/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum