Save the owner money by adding the sprinklers at a fair price, it's not your 
fault the GC is being unreasonable. I take it the "dead areas" not open on top 
to the area with the CC2's? Seems like the GC should get on board, maybe call 
them a future pipe chase or fill with insulation. What does the AHJ want?


Ron Fletcher
Aero Automatic
Phoenix, AZ



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Dewayne Martinez
Sent: Thursday, March 15, 2012 7:34 AM
To: [email protected]
Subject: RE: CC2/ RESIDENTIAL - AREA INCREASE

Small areas (under 10sf) that are framed out to make the tub / shower fit.  We 
have CC2 sprinklers in the combustible rated ceiling  space above but nothing 
figured for these dead areas.  The GC will not call these pipe chases because 
they do not contain pipe even though there is a rated floor above and below.  
He either wants them to have a sprinkler, be filled with insulation, or pick up 
3000SF design area.  We agreed to put sprinklers in the larger ones but many 
are only about 1.5 SF and it doesn't make sense to install them here.  Looking 
to add about
100 heads per floor (4 stories) and we are trying to find options to save the 
owner money. 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Thursday, March 15, 2012 9:12 AM
To: [email protected]
Subject: RE: CC2/ RESIDENTIAL - AREA INCREASE

Just curious. If the CC2 is being used in the combustible concealed space why 
would the 3000 sqft rule be an issue?


Ron Fletcher
Aero Automatic
Phoenix, AZ




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne Martinez
Sent: Thursday, March 15, 2012 6:44 AM
To: SprinklerFORUM
Subject: CC2/ RESIDENTIAL - AREA INCREASE

NFPA 13 (02ed) section 11.2.3.1.8 (3)

Does the 3000 SF area increase of this section apply to CC2 and
residential sprinklers?   I know NFPA 13 2010 provides some guidance but
this AHJ follows 2002.

 

Thanks,

Dewayne Martinez

Design Build Fire Protection

262-784-7900 (w)

262-784-8401 (f)

414-349-0468 (cell)

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120315/b91ccfc6/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to