Would it be an issue of hydraulically most remote vs physically most remote?
At 11:17 AM 4/3/2012, you wrote: >Got a submittal package where the contractor has two divided rooms. One is >0.40/3000 and adjacent room is .17/2000. He is calculating the .40 area and >has extended his hyd remote area beyond the wall of the room into the adjacent >.17 area and calced about 8 heads. >The .40 room is plenty large enough to allow the additional sprinklers to be >calced from within the room. > >Off the top of your head does anyone know where this type of thing is >addressed within NFPA 13? > >Craig L. Prahl, CET >Fire Protection >CH2MHILL >Lockwood Greene >1500 International Drive >Spartanburg, SC 29304-0491 >Direct - 864.599.4102 >Fax - 864.599.8439 >CH2MHILL Extension 74102 >[email protected] > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum Todd G. Williams, PE Fire Protection Design/Consulting Stonington, CT 860.535.2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum