B.  Always size to the actual system pipe volume.  This will be different
from the gpm required in the calc, and I have found with both SprinkCAD and
HydraCAD (don't know about MEPCAD or any others since I haven't worked with
em) that the system volume given needs to be checked.  They both provide an
answer, but not necessarily always an accurate one.

Bob Knight, CET III
208-318-3057
www.firebyknight.com



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, April 04, 2012 6:39 AM
To: [email protected]
Subject: Today's Challenge question - Sizing Air compressors

Ok, so for today here it is:

When sizing a system air compressor for a dry or preaction system you size
it based on:

(a) the volume that is shown on the hydraulic calculation provides,

(b) a takeoff of the piping and determine volume of the entire system from
the end head back to the system valve.