4" CMU partition between areas.  

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Tuesday, April 03, 2012 12:01 PM
To: [email protected]
Subject: RE: mixing densities in same calculated area

The calcs need to be redone to include a 3000 sqft remote area in the 0.40 
space. Hydraulically more remote. Is it a rated wall between the 0.17 and 0.40? 
K factors can be mixed (think regular heads and XCOV sidewalls). Also, read 
A11.2.3.2.1.1 (2002)





At 11:50 AM 4/3/2012, you wrote:
>But I don't have a 3000 sf design area for the 0.40 density area.  This is 
>palletized storage of group A plastic and Class IV commodities.  Total square 
>footage for the room is almost 5,000 sq. ft.
>
>Craig L. Prahl, CET   
>Fire Protection 
>CH2MHILL
>Lockwood Greene
>1500 International Drive
>Spartanburg, SC  29304-0491
>Direct - 864.599.4102
>Fax - 864.599.8439
>CH2MHILL Extension  74102
>[email protected]
>
>
>
>-----Original Message-----
>From: [email protected] 
>[mailto:[email protected]] On Behalf Of Cahill, 
>Christopher
>Sent: Tuesday, April 03, 2012 11:44 AM
>To: [email protected]
>Subject: RE: mixing densities in same calculated area
>
>Sounds like the difference between the room design method and the area density 
>method.  Stay within the room regardless of shape of RA or minimum length 
>along the BL?  I don't think the standard tells us which to use.   If they 
>crossed the wall sounds like area density and there are very specific rules on 
>the shape of the area.  And if the walls aren't rated the only choice the 
>designer has is 1.2 * 3,000^0.5.  If that takes them into the 0.17 area so be 
>it.  
>
>Chris Cahill, PE*
>Senior Fire Protection Engineer, Aviation & Facilities Group
>Burns & McDonnell
>8201 Norman Center Drive
>Bloomington, MN 55437
>Phone:  952.656.3652
>Fax:  952.229.2923
>[email protected]
>www.burnsmcd.com
>
>Proud to be one of FORTUNE's 100 Best Companies to Work For
>*Registered in: MN
>
>
>
>
>
>-----Original Message-----
>From: [email protected] 
>[mailto:[email protected]] On Behalf Of 
>[email protected]
>Sent: Tuesday, April 03, 2012 10:18 AM
>To: [email protected]
>Subject: mixing densities in same calculated area
>
>Got a submittal package where the contractor has two divided rooms.  One is 
>0.40/3000 and adjacent room is .17/2000.  He is calculating the .40 area and 
>has extended his hyd remote area beyond the wall of the room into the adjacent 
>.17 area and calced about 8 heads.
>The .40 room is plenty large enough to allow the additional sprinklers to be 
>calced from within the room.
>
>Off the top of your head does anyone know where this type of thing is 
>addressed within NFPA 13?
>
>Craig L. Prahl, CET   
>Fire Protection 
>CH2MHILL
>Lockwood Greene
>1500 International Drive
>Spartanburg, SC  29304-0491
>Direct - 864.599.4102
>Fax - 864.599.8439
>CH2MHILL Extension  74102
>[email protected]
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to