Would one option be just to consider it a floor opening still and provide a 
water curtain around it? 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Cahill, 
Christopher
Sent: Thursday, April 12, 2012 5:30 PM
To: [email protected]
Subject: RE: glass block floor - 1hr rating

Exactly, a 'substitution' to a code requirement is way different than a 
'performance' statement. 

Chris 



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Brad Casterline
Sent: Thursday, April 12, 2012 5:16 PM
To: [email protected]
Subject: RE: glass block floor - 1hr rating

IBC 2012, Table 601, comment d. (IBC 2006, Table 601, comment e).
~~ sprinklers can be used for substitution of 1-hour~~ in type IIA, IIIA, and 
VA. (since those just require one hour).

-----Original Message-----
From: Cahill, Christopher [mailto:[email protected]]
Sent: Thursday, April 12, 2012 5:05 PM
To: [email protected]
Subject: RE: glass block floor - 1hr rating

I'd like to see that section.  Barring a correction from a section that 
actually says that if you are talking about trade-ups the IBC says you can 
lower 1 hour requirements to 0.  It does not say 0 will achieve 1 hour when 
sprinklered.  Especially when in a LH you only need 30 minutes of water.
Yes, yes there are very few buildings with rating requirements and no OH.
But I have seen a few gov't buildings where the LH was the driving force on 
water because no room design method and you can pack a lot of sprinkler in the 
bathroom/locker/hallway cluster.  Last one was 27 or 28 heads in a 3,000 sq.ft. 
LH design.  

Again, I don't know everything show me your cards if you got them. 

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in: MN





-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad Casterline
Sent: Thursday, April 12, 2012 4:52 PM
To: [email protected]
Subject: RE: glass block floor - 1hr rating

There is a section in IBC that, given materials with no fire resistive ratings 
what so ever, just by sprinklering the building gives them a one hour 
resistance--- that may be something one could hang their hat on, But, there can 
no area or height increases taken ALSO. (increased travel dist. is still ok).

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to