There is for walls, but not floors. The code section below leads me to believe 
there are glass blocks that carry a rating.  Whoever is spec'ing the glass 
block will need to check the listing to see if they are listed for wall or 
floor use.

404.6 Enclosure of atriums. 
Atrium spaces shall be separated from adjacent spaces by a 1-hour fire barrier 
constructed in accordance with Section 707 or a horizontal assembly constructed 
in accordance with Section 711, or both. 

Exception: A fire barrier is not required where a glass wall forming a smoke 
partition is provided. The glass wall shall comply with all of the following: 

1. Automatic sprinklers are provided along both sides of the separation wall 
and doors, or on the room side only if there is not a walkway on the atrium 
side. The sprinklers shall be located between 4 inches and 12 inches (102 mm 
and 305 mm) away from the glass and at intervals along the glass not greater 
than 6 feet (1829 mm). The sprinkler system shall be designed so that the 
entire surface of the glass is wet upon activation of the sprinkler system 
without obstruction;
1.1. The glass wall shall be installed in a gasketed frame in a manner that the 
framing system deflects without breaking (loading) the glass before the 
sprinkler system operates; and
1.2. Where glass doors are provided in the glass wall, they shall be either 
self-closing or automatic-closing.
2. A fire barrier is not required where a glass-block wall assembly complying 
with Section 2110 and having a 3/4-hour fire protection rating is provided.
3. A fire barrier is not required between the atrium and the adjoining spaces 
of any three floors of the atrium provided such spaces are accounted for in the 
design of the smoke control system.



Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Dewayne Martinez [mailto:[email protected]] 
Sent: Thursday, April 12, 2012 4:48 PM
To: SprinklerFORUM
Subject: glass block floor - 1hr rating

Have a building where the architect wants to install a glass block floor
in lieu of an atrium opening but the floor needs to have a 1 hr rating.
Is there anywhere in the IBC/IFC/NFPA code that allows sprinkler
protection to provide the 1hr rating?

Thanks,

 

Dewayne Martinez

Design Build Fire Protection

262-784-7900 (w)

262-784-8401 (f)

414-349-0468 (cell)

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120412/eecaefc5/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to