The EPA is irrelevant for Reza's project.  If you look at the references in his 
original post, they are from European vendors so it's safe to say, he's not in 
Kansas.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Thompson, Pat
Sent: Monday, April 16, 2012 2:12 PM
To: [email protected]
Subject: RE: Aerosol vs Halocarbon/Inert extinguishing agents

Reza,
I must step in once again to point out that the key clause in your NFPA 2010 
reference is "agents approved for use in normally occupied spaces". Do you have 
data to show that any of the aerosols are approved for this application?  I 
would love to see it if you do. It is up to the manufactures to gain these 
approvals, then and only then can you apply the quoted reference.

As noted in my earlier post NFPA 2010 requires in that the agent be evaluated 
by the EPA SNAP program or equivalent, this is in Chapter 5 of the standard. A 
link to the EPA site was in my earlier email, check it out. Aerosols are not 
approved for normally occupied spaces. So this means that safety measures in 
Chapter 5 are not applicable, at least not until there is documented testing on 
the agent's safety.

Regards,




Pat Thompson
Special Hazard Sales
NICET #101475 
SimplexGrinnell
A Tyco International Company
907-743-9128 direct
907-561-4650 fax
[email protected] 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Reza Esmaeili
Sent: Saturday, April 14, 2012 1:06 AM
To: [email protected]
Subject: RE: Aerosol vs Halocarbon/Inert extinguishing agents

Thanks all for the professional replies.
I am not a professional, but while NFPA 2010 part 5.2.3.2.1 states that "In the 
event of failure of the predischarge alarm and time delay, means shall be 
provided to limit exposure to agents approved for use in normally occupied 
spaces to no longer than 5 minutes." So it is seems to be safe for human 
exposure below 5 minutes while not exceeding the adverse-effect level.
I agree that Halocarbon/Inert extinguishing agents are the first options, but 
Aerosol can works too.
 
Before posting this question in the forum, I was thinking that aerosol products 
like Pyrogen are only useful electrical switchboard cupboards or small 
electrical rooms or vessel engine rooms, but now I come to understand that 
although Aerosol is not the best option but where dust or residue is of lesser 
concern, they can be used for even larger rooms in total flooding use like pump 
rooms or paper archive rooms, but they are not suitable for server rooms 
because the residue may harm the hard disks.
 
Thanks for your nice comments.
Reza Esmaeili
Sarian System Novin Co., Ltd.
www.sarian.ir
 
 


--- On Sat, 4/14/12, Thompson, Pat <[email protected]> wrote:


From: Thompson, Pat <[email protected]>
Subject: RE: Aerosol vs Halocarbon/Inert extinguishing agents
To: "Smith, David L.(FAC)" <[email protected]>, 
[email protected]
Date: Saturday, April 14, 2012, 2:42 AM


Understand that this is my personal take on the subject; as with many
(most?) posts in the forum the statements made by individuals are opinions and 
should be taken on face value. I say this not to disparage the value of the 
forum; I believe that the collective experience and input of the participants 
is valuable indeed.

I have over 40 years in the fire protection industry and like all grey-haired 
fogies I have seen many things change over the years. For instance, there was a 
time that carbon tetrachloride was listed and commonly used in portable 
extinguishers. Anyone remember NFPA 12B? It was the standard for Halon 1211 
systems. Again, a product that was listed and used in its day that has gone 
bye-bye. There are more examples of products that  at their time had a listing 
(and even their own NFPA Standard) that we no longer use.

In my review of these aerosol products what jumps out at me is not what they 
say but what they infer. Nowhere do they state that they are listed as safe for 
human exposure, but the inference is clearly there. Why? - I can only surmise 
that it is because no data exists to substantiate it.
The only thing they state is that they are 'listed' and then they paint a 
picture that touts their 'advantages' over clean agents. It is a dangerous 
position to make the assumption that 'listed' makes them appropriate for a 
given application. The listing must be examined to determine what the product 
has been tested and 'listed' to do.  

Maybe it is a grey-haired characteristic or that I am skeptical by nature, but 
the presentation of information on the websites from the proponents of aerosols 
makes me suspicious.

A video clip of people breathing the aerosol only proves that no immediate 
toxicity is observed; but the inference is safety. Where's the testing and data 
(and/or 'listing') to support human exposure safety? I submit it does not 
exist. BTW- liver damage from carbon tet exposure was not immediately evident 
either.

Bottom line to this old fart is that aerosols may in fact have a place in fire 
protection, but until data is produced and listings established for their use 
in occupied spaces I'll be sticking to the clean agents that we have available.



Pat Thompson
Special Hazard Sales
NICET #101475
SimplexGrinnell
A Tyco International Company
907-743-9128 direct
907-561-4650 fax
[email protected] 


-----Original Message-----
From: Smith, David L.(FAC) [mailto:[email protected]] 
Sent: Thursday, April 12, 2012 3:49 PM
To: Thompson, Pat; [email protected]
Subject: Re: Aerosol vs Halocarbon/Inert extinguishing agents

Take s look at WWW.statx.com
And let us know what you thinks

Sent from my HTC on the Now Network from Sprint!


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120414/c96c95aa/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to