>From the NFPA 25 Handbook:
"Paragraph 5.2.2.3 provides an exemption from the inspection requirements for 
pipe and fittings in concealed spaces on the basis of two factors:
1. It is extremely costly and impractical to inspect piping in these spaces.
2. The inaccessibility of such piping means it is less likely to be damaged or 
otherwise affected
than piping in an open space.

When working in concealed spaces, however, it is a good idea to conduct an 
inspection of the
pipe and fittings in the space."

I'd be curious to see a quote for doing a visual inspection of all pipe and 
fittings above the ceilings in a 27 story office building.  



Also a couple of statements don't make sense:

"...it means that as far as I'm concerned the most hazardous spaces are 
inspection free."

"In this particular case, the water supply for the tower was completely out of 
action for 90 mins.  The electrical supply was on.  That means that the 
flooding water could have started a fire in any lower floor with
catastrophic consequences."



How are ceilings above an office space considered a "most hazardous space"?

Secondly, who do you figure flooding water was going to start a catastrophic 
fire?  Please don't say because the electricity was on...




Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Dan Arbel
Sent: Tuesday, April 17, 2012 6:31 AM
To: [email protected]
Subject: NFPA 25 - inspection above suspended ceiling

Dear Forum members,

I had a case of quick coupling failure in a  27 floors office tower.

The bolt holding the 3" coupling endured prolong corrosion (looks like
several years, that consumed 90% of the bolt section area.

There was no water dripping, just egress of a very small amount of water
from the joint that was enough to cause the failure, but not enough to be
detected "as a spreading wet stain on the ceiling elements.

It is possible to raise the ceiling element and observe the corrosion on
the coupling, but the maintenance contactors do not actually observe the
piping above the suspended ceiling.

Referring to NFPA 25,  Items 5.2.2.3:  Pipe and fittings installed in
concealed spaces such as above suspended ceilings shall not require
inspection.

A.5.2.2.3 Examples include some floor/ceiling or roof/ceiling assemblies,
areas under theater stages, pipe chases and other inaccessible areas.

It is stated elsewhere in the standard and the responsibility of the owner
is to afford accessibility.  So, non-accessible areas cannot be inspected.


However, if the interpretation of the standard calls for total exemption
for inspection in areas above suspended spaces,  it means that as far as
I'm concerned the most hazardous spaces are inspection free.

In this particular case, the water supply for the tower was completely out
of action for 90 mins.  The electrical supply was on.  That means that the
flooding water could have started a fire in any lower floor with
catastrophic consequences.

I would appreciate any response.

Dan



www.riskmanage.com

M: +972 (052) 6611337
T: +972 (04) 8243337
F: +972 (04) 8243278
Mail: [email protected]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to