Dan,

I'm not sure what Code Standard that building was built under but if we had a 
concealed space with that great of a load of combustibles, it would very likely 
be sprinklered.   

Flooding water may cause an arc or short circuit but if the water flow was 
continual it would seem hard to sustain any type of fire from the electrical 
equipment.  If the equipment is installed and maintained properly at some point 
the circuit protective devices should trip and de-energize the equipment 
automatically.   



Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Dan Arbel
Sent: Tuesday, April 17, 2012 3:17 PM
To: [email protected]
Subject: RE: NFPA 25 - inspection above suspended ceiling

How are ceilings above an office space considered a "most hazardous
space"?

Secondly, who do you figure flooding water was going to start a
catastrophic fire?  Please don't say because the electricity was on...

Dear Craig,

I assume that you run a great deal of fire investigations and none of them
involved fires in the ceiling plenum and you did not came across any case
of water raising fires. Therefore you find no sense in my statements.

Try to sprinkle some water on energized conductors.  You may imagine that
Moisture might cause electrical arching.  I had a couple of several $
million losses caused by moisture creating from water seeping from upper
floors.

Regarding plenums, the volume concentration of the fire loads to the
volume of the plenum may generate very high temperature. The fire load is
composed of electrical and communication cables.   Fire raisers are PL
Lamps and a great deal of electrical distribution boxes in above the
suspended ceiling.

Inspection above suspended ceiling is indeed very costly.  So are water
damages and fire occurring when all the detection systems and fire
sprinklers are off.

Dan



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, April 17, 2012 3:27 PM
To: [email protected]
Subject: RE: NFPA 25 - inspection above suspended ceiling

>From the NFPA 25 Handbook:
"Paragraph 5.2.2.3 provides an exemption from the inspection requirements
for pipe and fittings in concealed spaces on the basis of two factors:
1. It is extremely costly and impractical to inspect piping in these
spaces.
2. The inaccessibility of such piping means it is less likely to be
damaged or otherwise affected than piping in an open space.

When working in concealed spaces, however, it is a good idea to conduct an
inspection of the pipe and fittings in the space."

I'd be curious to see a quote for doing a visual inspection of all pipe
and fittings above the ceilings in a 27 story office building.



Also a couple of statements don't make sense:

"...it means that as far as I'm concerned the most hazardous spaces are
inspection free."

"In this particular case, the water supply for the tower was completely
out of action for 90 mins.  The electrical supply was on.  That means that
the flooding water could have started a fire in any lower floor with
catastrophic consequences."



How are ceilings above an office space considered a "most hazardous
space"?

Secondly, who do you figure flooding water was going to start a
catastrophic fire?  Please don't say because the electricity was on...




Craig L. Prahl, CET
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dan Arbel
Sent: Tuesday, April 17, 2012 6:31 AM
To: [email protected]
Subject: NFPA 25 - inspection above suspended ceiling

Dear Forum members,

I had a case of quick coupling failure in a  27 floors office tower.

The bolt holding the 3" coupling endured prolong corrosion (looks like
several years, that consumed 90% of the bolt section area.

There was no water dripping, just egress of a very small amount of water
from the joint that was enough to cause the failure, but not enough to be
detected "as a spreading wet stain on the ceiling elements.

It is possible to raise the ceiling element and observe the corrosion on
the coupling, but the maintenance contactors do not actually observe the
piping above the suspended ceiling.

Referring to NFPA 25,  Items 5.2.2.3:  Pipe and fittings installed in
concealed spaces such as above suspended ceilings shall not require
inspection.

A.5.2.2.3 Examples include some floor/ceiling or roof/ceiling assemblies,
areas under theater stages, pipe chases and other inaccessible areas.

It is stated elsewhere in the standard and the responsibility of the owner
is to afford accessibility.  So, non-accessible areas cannot be inspected.


However, if the interpretation of the standard calls for total exemption
for inspection in areas above suspended spaces,  it means that as far as
I'm concerned the most hazardous spaces are inspection free.

In this particular case, the water supply for the tower was completely out
of action for 90 mins.  The electrical supply was on.  That means that the
flooding water could have started a fire in any lower floor with
catastrophic consequences.

I would appreciate any response.

Dan



www.riskmanage.com

M: +972 (052) 6611337
T: +972 (04) 8243337
F: +972 (04) 8243278
Mail: [email protected]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to