We actually did a project where the engineer specified access panels at each 
grooved coupling for maintenance (I wanted to bid on that maintenance 
contract). He gave up when faced with the impossibility of providing a useable 
access panel for grooved couplings 15 ft above a gyp rock ceiling with all 
manner of duct and conduit between the ceiling and the coupling.

One catastrophic coupling failure out of the millions that are installed every 
year isn't too bad.

Ron Fletcher
Aero Automatic
Phoenix, AZ



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Dan Arbel
Sent: Tuesday, April 17, 2012 12:17 PM
To: [email protected]
Subject: RE: NFPA 25 - inspection above suspended ceiling

How are ceilings above an office space considered a "most hazardous space"?

Secondly, who do you figure flooding water was going to start a catastrophic 
fire?  Please don't say because the electricity was on...

Dear Craig,

I assume that you run a great deal of fire investigations and none of them 
involved fires in the ceiling plenum and you did not came across any case of 
water raising fires. Therefore you find no sense in my statements.

Try to sprinkle some water on energized conductors.  You may imagine that 
Moisture might cause electrical arching.  I had a couple of several $ million 
losses caused by moisture creating from water seeping from upper floors.

Regarding plenums, the volume concentration of the fire loads to the volume of 
the plenum may generate very high temperature. The fire load is
composed of electrical and communication cables.   Fire raisers are PL
Lamps and a great deal of electrical distribution boxes in above the suspended 
ceiling.

Inspection above suspended ceiling is indeed very costly.  So are water damages 
and fire occurring when all the detection systems and fire sprinklers are off.

Dan



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, April 17, 2012 3:27 PM
To: [email protected]
Subject: RE: NFPA 25 - inspection above suspended ceiling

>From the NFPA 25 Handbook:
"Paragraph 5.2.2.3 provides an exemption from the inspection requirements for 
pipe and fittings in concealed spaces on the basis of two factors:
1. It is extremely costly and impractical to inspect piping in these spaces.
2. The inaccessibility of such piping means it is less likely to be damaged or 
otherwise affected than piping in an open space.

When working in concealed spaces, however, it is a good idea to conduct an 
inspection of the pipe and fittings in the space."

I'd be curious to see a quote for doing a visual inspection of all pipe and 
fittings above the ceilings in a 27 story office building.



Also a couple of statements don't make sense:

"...it means that as far as I'm concerned the most hazardous spaces are 
inspection free."

"In this particular case, the water supply for the tower was completely out of 
action for 90 mins.  The electrical supply was on.  That means that the 
flooding water could have started a fire in any lower floor with catastrophic 
consequences."



How are ceilings above an office space considered a "most hazardous space"?

Secondly, who do you figure flooding water was going to start a catastrophic 
fire?  Please don't say because the electricity was on...




Craig L. Prahl, CET
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dan Arbel
Sent: Tuesday, April 17, 2012 6:31 AM
To: [email protected]
Subject: NFPA 25 - inspection above suspended ceiling

Dear Forum members,

I had a case of quick coupling failure in a  27 floors office tower.

The bolt holding the 3" coupling endured prolong corrosion (looks like several 
years, that consumed 90% of the bolt section area.

There was no water dripping, just egress of a very small amount of water from 
the joint that was enough to cause the failure, but not enough to be detected 
"as a spreading wet stain on the ceiling elements.

It is possible to raise the ceiling element and observe the corrosion on the 
coupling, but the maintenance contactors do not actually observe the piping 
above the suspended ceiling.

Referring to NFPA 25,  Items 5.2.2.3:  Pipe and fittings installed in concealed 
spaces such as above suspended ceilings shall not require inspection.

A.5.2.2.3 Examples include some floor/ceiling or roof/ceiling assemblies, areas 
under theater stages, pipe chases and other inaccessible areas.

It is stated elsewhere in the standard and the responsibility of the owner is 
to afford accessibility.  So, non-accessible areas cannot be inspected.


However, if the interpretation of the standard calls for total exemption for 
inspection in areas above suspended spaces,  it means that as far as I'm 
concerned the most hazardous spaces are inspection free.

In this particular case, the water supply for the tower was completely out of 
action for 90 mins.  The electrical supply was on.  That means that the 
flooding water could have started a fire in any lower floor with catastrophic 
consequences.

I would appreciate any response.

Dan



www.riskmanage.com

M: +972 (052) 6611337
T: +972 (04) 8243337
F: +972 (04) 8243278
Mail: [email protected]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to