I heard more about this today from an Illinois plumbing inspector. For those interested, they (or maybe just he) consider a fire hydrant as a device to which applies Part 890 Plumbing Code Section 890.1140 "Special Applications and Installations". The catching sections are 890.1140 e) 1) and 890.1140 e) 2) A) i). All the applications and installations mentioned by this section, i.e. that which are special, are hose outlets, yard hydrants with weeps, flush valves, laundry machines, dishwashers, medical water aspirators, mobile homes and carbonated beverage machines.

One would think that section title "Special Applications and Installations" intends to single out specifically named applications and installations. For example there is a trade distinction between Yard Hydrants and Fire Hydrants that any reasonable tradesman would know. If this code truly intends to apply to both Yard Hydrants and Fire Hydrants then it would not be "special" and the wording would be "Hydrants". Incidentally there is no mention of any fire protection related devices at all in the section. All mention of fire protection devices, which surely must have special distinction to most, occurs in a different 890 subsection. Claiming this section applies also to fire protection is to expand its special scope to included another very special application, thereby denying the section's purpose.

The question stills stands for those in the Illinois area. Is this actually the state's stance? For the case where I heard about this, the "state" will be making another arm of the "state" put an RPZ device in a hot box on the piping between an ordinary, existing fire hydrant and the private main it connects to, because that one hydrant is being moved due to a new drive and that section of existing underground is being replace, not as its own small project but as part of a much larger project.

Allan Seidel
St. Louis, MO

On Jun 6, 2012, at 8:13 AM, <[email protected]> wrote:

The 2006 Uniform Plumbing Code 603.4.16.1requires backflows in lines to FP systems. RPZ's are required for systems with chemicals like antifreeze or AFFF and double checks for others. It says they are not required for private hydrant only lines that comply with city water main and AWWA standards.

To the best of my knowledge there is no requirement in the International Plumbing Code.


Ron Fletcher
Aero Automatic
Phoenix, AZ




-----Original Message-----
From: [email protected] [mailto:[email protected] ] On Behalf Of Timothy W Goins
Sent: Wednesday, June 06, 2012 5:40 AM
To: [email protected]
Subject: Re: RPZ for a dedicated private underground fire mains having fire hydrants

Most THINK that the AWWA recommends BFP's on ALL firelines, especially deadened lines over 100 feet, but the AWWA does NOT recommend backflow protection on hydrant only lines.

"For I am not ashamed of the gospel , , because it is God’s power for salvation to everyone who believes..." HCS Romans 1:16

On Jun 6, 2012, at 12:56 AM, [email protected] wrote:

accounting departments see plus signs when they see marketing department, lunch n learn, and regulatory agencies on the same spread sheet line lol (and some consulting engineering firms). Steve- can you explain the USC friction loss graphs? there is some diff in turning on and turning off?
Quoting Ron Greenman <[email protected]>:

I think the backflow prevention device manufacturers have a lot of
influence with a fair share of regulatory agencies.

On Tue, Jun 5, 2012 at 9:05 PM, Steve Leyton <[email protected] >wrote:

Private fire service mains in CA have required backflows for years.
The type of device varies by water authority standards, but pretty
much throughout Southern California the use of an RPDA is standard practice.
Whether the downstream connections are sprinklers only, plus one
hydrant or with multiple hydrants, a backflow appliance is required on a private fire service main. The thinking isn't that hydrants represent a cross
connection or contamination threat per se, but that a private
property owner can make whatever connections they want in the dark of night after final acceptance testing. So better safe than sorry, bureaucratically
speaking ...

SML
In SoCal, where nothing surprises anymore

________________________________

From: [email protected] on behalf of
AKS-Gmail-IMAP
Sent: Tue 6/5/2012 7:24 PM
To: [email protected]
Subject: RPZ for a dedicated private underground fire mains having
fire hydrants



I am hearing that in Illinois the state plumbing inspectors insist
on RPZ back flow prevention for fire hydrants on dedicated
underground private service mains. What is up with that?

Allan Seidel
St. Louis. MO
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


-------------- next part -------------- A non-text attachment was
scrubbed...
Name: winmail.dat
Type: application/ms-tnef
Size: 4685 bytes
Desc: not available
URL: <
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/ att
achments/20120605/c0c6b675/attachment.bin

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum




--
Ron Greenman
Instructor
Fire Protection Engineering Technology Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
-------------- next part -------------- An HTML attachment was
scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/ att
achments/20120605/19d8453d/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120606/015d1967/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to