Hey Steve have you been on the design end of a Fire Protection System using 
reclaimed water? If you have wanted to know what issues you ran across if any?

----- Original Message -----
From: Steve Leyton [mailto:[email protected]]
Sent: Thursday, June 07, 2012 09:33 AM
To: [email protected] <[email protected]>
Subject: RE: RPZ for a dedicated private underground fire mains having fire 
hydrants

Well ... as ridiculous as all this may sound ...

In SoCal, we have water districts that are moving hard into reclaimed
water.   Golf courses and public green areas such as parks and right of
way planters and medians, are being irrigated with reclaimed.  Easiest
and most obvious application for RW as it can work quite well at low
residual pressures.   But water wise thinking being as it is, and
bureaucracy being as IT is, we are now seeing reclaimed used for fire
water.  And of course, the California Dept. of Health has a few opinions
on what you have to do with fire apparatus that has pumped RW, such as
completely clean and flush.   So a BFP on a public hydrant, or on FD
suction hose is the next logical legislative "solution".

SML 




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Art
Tiroly
Sent: Thursday, June 07, 2012 9:29 AM
To: [email protected]
Subject: RE: RPZ for a dedicated private underground fire mains having
fire hydrants

Then should public street hydrants need BFP installed? 


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
AKS-Gmail-IMAP
Sent: Wednesday, June 06, 2012 10:49 PM
To: [email protected]
Subject: Re: RPZ for a dedicated private underground fire mains having
fire hydrants

I heard more about this today from an Illinois plumbing inspector. For
those interested, they (or maybe just he) consider a fire hydrant as a
device to which applies Part 890 Plumbing Code Section 890.1140 "Special
Applications and Installations". The catching sections are 890.1140 e)
1) and 890.1140 e)
2) A) i). All the applications and installations mentioned by this
section, i.e. that which are special, are hose outlets, yard hydrants
with weeps, flush valves, laundry machines, dishwashers, medical water
aspirators, mobile homes and carbonated beverage machines.

One would think that section title "Special Applications and
Installations"
intends to single out specifically named applications and installations.
For example there is a trade distinction between Yard Hydrants and Fire
Hydrants that any reasonable tradesman would know. If this code truly
intends to apply to both Yard Hydrants and Fire Hydrants then it would
not be "special"
and the wording would be "Hydrants". Incidentally there is no mention of
any fire protection related devices at all in the section. All mention
of fire protection devices, which surely must have special distinction
to most, occurs in a different 890 subsection. Claiming this section
applies also to fire protection is to expand its special scope to
included another very special application, thereby denying the section's
purpose.

The question stills stands for those in the Illinois area. Is this
actually the state's stance? For the case where I heard about this, the
"state" will be making another arm of the "state" put an RPZ device in a
hot box on the piping between an ordinary, existing fire hydrant and the
private main it connects to, because that one hydrant is being moved due
to a new drive and that section of existing underground is being
replace, not as its own small project but as part of a much larger
project.

Allan Seidel
St. Louis, MO

On Jun 6, 2012, at 8:13 AM, <[email protected]> wrote:

> The 2006 Uniform Plumbing Code 603.4.16.1requires backflows in lines 
> to FP systems. RPZ's are required for systems with chemicals like 
> antifreeze or AFFF and double checks for others. It says they are not 
> required for private hydrant only lines that comply with city water 
> main and AWWA standards.
>
> To the best of my knowledge there is no requirement in the 
> International Plumbing Code.
>
>
> Ron Fletcher
> Aero Automatic
> Phoenix, AZ
>
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]
> ] On Behalf Of Timothy W Goins
> Sent: Wednesday, June 06, 2012 5:40 AM
> To: [email protected]
> Subject: Re: RPZ for a dedicated private underground fire mains having

> fire hydrants
>
> Most THINK that the AWWA recommends BFP's on ALL firelines, especially

> deadened lines over 100 feet, but the AWWA does NOT recommend backflow

> protection on hydrant only lines.
>
> "For I am not ashamed of the gospel , , because it is God's power for 
> salvation to everyone who believes..." HCS Romans 1:16
>
> On Jun 6, 2012, at 12:56 AM, [email protected] wrote:
>
>> accounting departments see plus signs when they see marketing 
>> department, lunch n learn, and regulatory agencies on the same spread

>> sheet line lol (and some consulting engineering firms).
>> Steve- can you explain the USC friction loss graphs? there is some 
>> diff in turning on and turning off?
>> Quoting Ron Greenman <[email protected]>:
>>
>>> I think the backflow prevention device manufacturers have a lot of 
>>> influence with a fair share of regulatory agencies.
>>>
>>> On Tue, Jun 5, 2012 at 9:05 PM, Steve Leyton 
>>> <[email protected]
>>> >wrote:
>>>
>>>> Private fire service mains in CA have required backflows for years.
>>>> The type of device varies by water authority standards, but pretty 
>>>> much throughout Southern California the use of an RPDA is standard 
>>>> practice.
>>>> Whether the downstream connections are sprinklers only, plus one 
>>>> hydrant or with multiple hydrants, a backflow appliance is required

>>>> on a private
>>>> fire service main.   The thinking isn't that hydrants represent a  
>>>> cross
>>>> connection or contamination threat per se, but that a private 
>>>> property owner can make whatever connections they want in the dark 
>>>> of night after
>>>> final acceptance testing.   So better safe than sorry,  
>>>> bureaucratically
>>>> speaking ...
>>>>
>>>> SML
>>>> In SoCal, where nothing surprises anymore
>>>>
>>>> ________________________________
>>>>
>>>> From: [email protected] on behalf of 
>>>> AKS-Gmail-IMAP
>>>> Sent: Tue 6/5/2012 7:24 PM
>>>> To: [email protected]
>>>> Subject: RPZ for a dedicated private underground fire mains having 
>>>> fire hydrants
>>>>
>>>>
>>>>
>>>> I am hearing that in Illinois the state plumbing inspectors insist 
>>>> on RPZ back flow prevention for fire hydrants on dedicated 
>>>> underground private service mains. What is up with that?
>>>>
>>>> Allan Seidel
>>>> St. Louis. MO
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>
>>>>
>>>> -------------- next part -------------- A non-text attachment was 
>>>> scrubbed...
>>>> Name: winmail.dat
>>>> Type: application/ms-tnef
>>>> Size: 4685 bytes
>>>> Desc: not available
>>>> URL: <
>>>> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/
>>>> att
>>>> achments/20120605/c0c6b675/attachment.bin
>>>>>
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>
>>>
>>>
>>>
>>> --
>>> Ron Greenman
>>> Instructor
>>> Fire Protection Engineering Technology Bates Technical College
>>> 1101 So. Yakima Ave.
>>> Tacoma, WA 98405
>>>
>>> [email protected]
>>>
>>> http://www.bates.ctc.edu/fireprotection/
>>>
>>> 253.680.7346
>>> 253.576.9700 (cell)
>>>
>>> Member:
>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>>>
>>> They are happy men whose natures sort with their vocations. -Francis

>>> Bacon, essayist, philosopher, and statesman (1561-1626)
>>> -------------- next part -------------- An HTML attachment was 
>>> scrubbed...
>>> URL:
>>> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/
>>> att
>>> achments/20120605/19d8453d/attachment.html>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ment
s/20120606/015d1967/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum