Really RW?  We have a few problems with corrosion and MIC in potable water.  
What else might be in these RW system that is going to eat up our systems or I 
suppose might be better as a slim chance.  Can the chemical makeup of RW change 
over time and seasons further complicating what is does to our systems? 

What's the FD going to wash and flush?

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN





-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve Leyton
Sent: Thursday, June 07, 2012 11:53 AM
To: [email protected]
Subject: RE: RPZ for a dedicated private underground fire mains having fire 
hydrants

We are doing our first building system off RW at this time.  From our due 
diligence for the current project, we learned that in NorCal, there have been a 
few building systems connected to reclaimed.  There are some in the 
Dublin/Pleasanton/Livermore area, if I recall correctly (Tom
McKinnon are you out there?).   We've been told by the water purveyor
that no special treatment is required, but the fire dept. wants a wash &
flush station on the property.   We're configuring the site main with
BFP's as if the source main was potable, and on paper everything looks utterly 
conventional.

SML




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Letterman, Todd
Sent: Thursday, June 07, 2012 9:38 AM
To: '[email protected]'
Subject: Re: RPZ for a dedicated private underground fire mains having fire 
hydrants

Hey Steve have you been on the design end of a Fire Protection System using 
reclaimed water? If you have wanted to know what issues you ran across if any?

----- Original Message -----
From: Steve Leyton [mailto:[email protected]]
Sent: Thursday, June 07, 2012 09:33 AM
To: [email protected] <[email protected]>
Subject: RE: RPZ for a dedicated private underground fire mains having fire 
hydrants

Well ... as ridiculous as all this may sound ...

In SoCal, we have water districts that are moving hard into reclaimed
water.   Golf courses and public green areas such as parks and right of
way planters and medians, are being irrigated with reclaimed.  Easiest and most 
obvious application for RW as it can work quite well at low
residual pressures.   But water wise thinking being as it is, and
bureaucracy being as IT is, we are now seeing reclaimed used for fire water.  
And of course, the California Dept. of Health has a few opinions on what you 
have to do with fire apparatus that has pumped RW, such as
completely clean and flush.   So a BFP on a public hydrant, or on FD
suction hose is the next logical legislative "solution".

SML 




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Art Tiroly
Sent: Thursday, June 07, 2012 9:29 AM
To: [email protected]
Subject: RE: RPZ for a dedicated private underground fire mains having fire 
hydrants

Then should public street hydrants need BFP installed? 


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of AKS-Gmail-IMAP
Sent: Wednesday, June 06, 2012 10:49 PM
To: [email protected]
Subject: Re: RPZ for a dedicated private underground fire mains having fire 
hydrants

I heard more about this today from an Illinois plumbing inspector. For those 
interested, they (or maybe just he) consider a fire hydrant as a device to 
which applies Part 890 Plumbing Code Section 890.1140 "Special Applications and 
Installations". The catching sections are 890.1140 e)
1) and 890.1140 e)
2) A) i). All the applications and installations mentioned by this section, 
i.e. that which are special, are hose outlets, yard hydrants with weeps, flush 
valves, laundry machines, dishwashers, medical water aspirators, mobile homes 
and carbonated beverage machines.

One would think that section title "Special Applications and Installations"
intends to single out specifically named applications and installations.
For example there is a trade distinction between Yard Hydrants and Fire 
Hydrants that any reasonable tradesman would know. If this code truly intends 
to apply to both Yard Hydrants and Fire Hydrants then it would not be "special"
and the wording would be "Hydrants". Incidentally there is no mention of any 
fire protection related devices at all in the section. All mention of fire 
protection devices, which surely must have special distinction to most, occurs 
in a different 890 subsection. Claiming this section applies also to fire 
protection is to expand its special scope to included another very special 
application, thereby denying the section's purpose.

The question stills stands for those in the Illinois area. Is this actually the 
state's stance? For the case where I heard about this, the "state" will be 
making another arm of the "state" put an RPZ device in a hot box on the piping 
between an ordinary, existing fire hydrant and the private main it connects to, 
because that one hydrant is being moved due to a new drive and that section of 
existing underground is being replace, not as its own small project but as part 
of a much larger project.

Allan Seidel
St. Louis, MO

On Jun 6, 2012, at 8:13 AM, <[email protected]> wrote:

> The 2006 Uniform Plumbing Code 603.4.16.1requires backflows in lines 
> to FP systems. RPZ's are required for systems with chemicals like 
> antifreeze or AFFF and double checks for others. It says they are not 
> required for private hydrant only lines that comply with city water 
> main and AWWA standards.
>
> To the best of my knowledge there is no requirement in the 
> International Plumbing Code.
>
>
> Ron Fletcher
> Aero Automatic
> Phoenix, AZ
>
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]
> ] On Behalf Of Timothy W Goins
> Sent: Wednesday, June 06, 2012 5:40 AM
> To: [email protected]
> Subject: Re: RPZ for a dedicated private underground fire mains having

> fire hydrants
>
> Most THINK that the AWWA recommends BFP's on ALL firelines, especially

> deadened lines over 100 feet, but the AWWA does NOT recommend backflow

> protection on hydrant only lines.
>
> "For I am not ashamed of the gospel , , because it is God's power for 
> salvation to everyone who believes..." HCS Romans 1:16
>
> On Jun 6, 2012, at 12:56 AM, [email protected] wrote:
>
>> accounting departments see plus signs when they see marketing 
>> department, lunch n learn, and regulatory agencies on the same spread

>> sheet line lol (and some consulting engineering firms).
>> Steve- can you explain the USC friction loss graphs? there is some 
>> diff in turning on and turning off?
>> Quoting Ron Greenman <[email protected]>:
>>
>>> I think the backflow prevention device manufacturers have a lot of 
>>> influence with a fair share of regulatory agencies.
>>>
>>> On Tue, Jun 5, 2012 at 9:05 PM, Steve Leyton 
>>> <[email protected]
>>> >wrote:
>>>
>>>> Private fire service mains in CA have required backflows for years.
>>>> The type of device varies by water authority standards, but pretty 
>>>> much throughout Southern California the use of an RPDA is standard 
>>>> practice.
>>>> Whether the downstream connections are sprinklers only, plus one 
>>>> hydrant or with multiple hydrants, a backflow appliance is required

>>>> on a private
>>>> fire service main.   The thinking isn't that hydrants represent a  
>>>> cross
>>>> connection or contamination threat per se, but that a private 
>>>> property owner can make whatever connections they want in the dark 
>>>> of night after
>>>> final acceptance testing.   So better safe than sorry,  
>>>> bureaucratically
>>>> speaking ...
>>>>
>>>> SML
>>>> In SoCal, where nothing surprises anymore
>>>>
>>>> ________________________________
>>>>
>>>> From: [email protected] on behalf of 
>>>> AKS-Gmail-IMAP
>>>> Sent: Tue 6/5/2012 7:24 PM
>>>> To: [email protected]
>>>> Subject: RPZ for a dedicated private underground fire mains having 
>>>> fire hydrants
>>>>
>>>>
>>>>
>>>> I am hearing that in Illinois the state plumbing inspectors insist 
>>>> on RPZ back flow prevention for fire hydrants on dedicated 
>>>> underground private service mains. What is up with that?
>>>>
>>>> Allan Seidel
>>>> St. Louis. MO
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>
>>>>
>>>> -------------- next part -------------- A non-text attachment was 
>>>> scrubbed...
>>>> Name: winmail.dat
>>>> Type: application/ms-tnef
>>>> Size: 4685 bytes
>>>> Desc: not available
>>>> URL: <
>>>> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/
>>>> att
>>>> achments/20120605/c0c6b675/attachment.bin
>>>>>
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>
>>>
>>>
>>>
>>> --
>>> Ron Greenman
>>> Instructor
>>> Fire Protection Engineering Technology Bates Technical College
>>> 1101 So. Yakima Ave.
>>> Tacoma, WA 98405
>>>
>>> [email protected]
>>>
>>> http://www.bates.ctc.edu/fireprotection/
>>>
>>> 253.680.7346
>>> 253.576.9700 (cell)
>>>
>>> Member:
>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>>>
>>> They are happy men whose natures sort with their vocations. -Francis

>>> Bacon, essayist, philosopher, and statesman (1561-1626)
>>> -------------- next part -------------- An HTML attachment was 
>>> scrubbed...
>>> URL:
>>> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/
>>> att
>>> achments/20120605/19d8453d/attachment.html>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ment
s/20120606/015d1967/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to