Steve,

Next time we are imbibing together remind me to tell you the story about:
The Washing of the Raytheon Building at the Naval Undersea Warfare Center
in Keyport and the Brain of the Enviro Nazi.

On Thu, Jun 7, 2012 at 10:17 AM, Steve Leyton <[email protected]>wrote:

> Dude:
>
> It's a GOVERNMENT REGULATION.  I have no idea what's to wash or flush;
> chances are there's no value to this additional layer of cost and hassle.
> Next question: where does this filthy run-off go?  Not to the storm drain
> system I hope; the otters will be slowly poisoned.
>
> Steve
>
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Cahill, Christopher
> Sent: Thursday, June 07, 2012 10:10 AM
> To: [email protected]
> Subject: RE: RPZ for a dedicated private underground fire mains having
> fire hydrants
>
> Really RW?  We have a few problems with corrosion and MIC in potable
> water.  What else might be in these RW system that is going to eat up our
> systems or I suppose might be better as a slim chance.  Can the chemical
> makeup of RW change over time and seasons further complicating what is does
> to our systems?
>
> What's the FD going to wash and flush?
>
> Chris Cahill, PE*
> Senior Fire Protection Engineer, Aviation & Facilities Group Burns &
> McDonnell
> 8201 Norman Center Drive
> Bloomington, MN 55437
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]
> www.burnsmcd.com
>
> Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered
> in: MN
>
>
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Steve Leyton
> Sent: Thursday, June 07, 2012 11:53 AM
> To: [email protected]
> Subject: RE: RPZ for a dedicated private underground fire mains having
> fire hydrants
>
> We are doing our first building system off RW at this time.  From our due
> diligence for the current project, we learned that in NorCal, there have
> been a few building systems connected to reclaimed.  There are some in the
> Dublin/Pleasanton/Livermore area, if I recall correctly (Tom
> McKinnon are you out there?).   We've been told by the water purveyor
> that no special treatment is required, but the fire dept. wants a wash &
> flush station on the property.   We're configuring the site main with
> BFP's as if the source main was potable, and on paper everything looks
> utterly conventional.
>
> SML
>
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Letterman,
> Todd
> Sent: Thursday, June 07, 2012 9:38 AM
> To: '[email protected]'
> Subject: Re: RPZ for a dedicated private underground fire mains having
> fire hydrants
>
> Hey Steve have you been on the design end of a Fire Protection System
> using reclaimed water? If you have wanted to know what issues you ran
> across if any?
>
> ----- Original Message -----
> From: Steve Leyton [mailto:[email protected]]
> Sent: Thursday, June 07, 2012 09:33 AM
> To: [email protected] <[email protected]>
> Subject: RE: RPZ for a dedicated private underground fire mains having
> fire hydrants
>
> Well ... as ridiculous as all this may sound ...
>
> In SoCal, we have water districts that are moving hard into reclaimed
> water.   Golf courses and public green areas such as parks and right of
> way planters and medians, are being irrigated with reclaimed.  Easiest and
> most obvious application for RW as it can work quite well at low
> residual pressures.   But water wise thinking being as it is, and
> bureaucracy being as IT is, we are now seeing reclaimed used for fire
> water.  And of course, the California Dept. of Health has a few opinions on
> what you have to do with fire apparatus that has pumped RW, such as
> completely clean and flush.   So a BFP on a public hydrant, or on FD
> suction hose is the next logical legislative "solution".
>
> SML
>
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Art Tiroly
> Sent: Thursday, June 07, 2012 9:29 AM
> To: [email protected]
> Subject: RE: RPZ for a dedicated private underground fire mains having
> fire hydrants
>
> Then should public street hydrants need BFP installed?
>
>
> Arthur Tiroly
> ATCO Fire Protection Design
> Tiroly and Associates
> 24400 Highland Rd rm 25, CLE 44143
> 216-621-8899
> 216-570-7030 Cell
> WWW.ATCOfirepro.com
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> AKS-Gmail-IMAP
> Sent: Wednesday, June 06, 2012 10:49 PM
> To: [email protected]
> Subject: Re: RPZ for a dedicated private underground fire mains having
> fire hydrants
>
> I heard more about this today from an Illinois plumbing inspector. For
> those interested, they (or maybe just he) consider a fire hydrant as a
> device to which applies Part 890 Plumbing Code Section 890.1140 "Special
> Applications and Installations". The catching sections are 890.1140 e)
> 1) and 890.1140 e)
> 2) A) i). All the applications and installations mentioned by this
> section, i.e. that which are special, are hose outlets, yard hydrants with
> weeps, flush valves, laundry machines, dishwashers, medical water
> aspirators, mobile homes and carbonated beverage machines.
>
> One would think that section title "Special Applications and Installations"
> intends to single out specifically named applications and installations.
> For example there is a trade distinction between Yard Hydrants and Fire
> Hydrants that any reasonable tradesman would know. If this code truly
> intends to apply to both Yard Hydrants and Fire Hydrants then it would not
> be "special"
> and the wording would be "Hydrants". Incidentally there is no mention of
> any fire protection related devices at all in the section. All mention of
> fire protection devices, which surely must have special distinction to
> most, occurs in a different 890 subsection. Claiming this section applies
> also to fire protection is to expand its special scope to included another
> very special application, thereby denying the section's purpose.
>
> The question stills stands for those in the Illinois area. Is this
> actually the state's stance? For the case where I heard about this, the
> "state" will be making another arm of the "state" put an RPZ device in a
> hot box on the piping between an ordinary, existing fire hydrant and the
> private main it connects to, because that one hydrant is being moved due to
> a new drive and that section of existing underground is being replace, not
> as its own small project but as part of a much larger project.
>
> Allan Seidel
> St. Louis, MO
>
> On Jun 6, 2012, at 8:13 AM, <[email protected]> wrote:
>
> > The 2006 Uniform Plumbing Code 603.4.16.1requires backflows in lines
> > to FP systems. RPZ's are required for systems with chemicals like
> > antifreeze or AFFF and double checks for others. It says they are not
> > required for private hydrant only lines that comply with city water
> > main and AWWA standards.
> >
> > To the best of my knowledge there is no requirement in the
> > International Plumbing Code.
> >
> >
> > Ron Fletcher
> > Aero Automatic
> > Phoenix, AZ
> >
> >
> >
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]
> > ] On Behalf Of Timothy W Goins
> > Sent: Wednesday, June 06, 2012 5:40 AM
> > To: [email protected]
> > Subject: Re: RPZ for a dedicated private underground fire mains having
>
> > fire hydrants
> >
> > Most THINK that the AWWA recommends BFP's on ALL firelines, especially
>
> > deadened lines over 100 feet, but the AWWA does NOT recommend backflow
>
> > protection on hydrant only lines.
> >
> > "For I am not ashamed of the gospel , , because it is God's power for
> > salvation to everyone who believes..." HCS Romans 1:16
> >
> > On Jun 6, 2012, at 12:56 AM, [email protected] wrote:
> >
> >> accounting departments see plus signs when they see marketing
> >> department, lunch n learn, and regulatory agencies on the same spread
>
> >> sheet line lol (and some consulting engineering firms).
> >> Steve- can you explain the USC friction loss graphs? there is some
> >> diff in turning on and turning off?
> >> Quoting Ron Greenman <[email protected]>:
> >>
> >>> I think the backflow prevention device manufacturers have a lot of
> >>> influence with a fair share of regulatory agencies.
> >>>
> >>> On Tue, Jun 5, 2012 at 9:05 PM, Steve Leyton
> >>> <[email protected]
> >>> >wrote:
> >>>
> >>>> Private fire service mains in CA have required backflows for years.
> >>>> The type of device varies by water authority standards, but pretty
> >>>> much throughout Southern California the use of an RPDA is standard
> >>>> practice.
> >>>> Whether the downstream connections are sprinklers only, plus one
> >>>> hydrant or with multiple hydrants, a backflow appliance is required
>
> >>>> on a private
> >>>> fire service main.   The thinking isn't that hydrants represent a
> >>>> cross
> >>>> connection or contamination threat per se, but that a private
> >>>> property owner can make whatever connections they want in the dark
> >>>> of night after
> >>>> final acceptance testing.   So better safe than sorry,
> >>>> bureaucratically
> >>>> speaking ...
> >>>>
> >>>> SML
> >>>> In SoCal, where nothing surprises anymore
> >>>>
> >>>> ________________________________
> >>>>
> >>>> From: [email protected] on behalf of
> >>>> AKS-Gmail-IMAP
> >>>> Sent: Tue 6/5/2012 7:24 PM
> >>>> To: [email protected]
> >>>> Subject: RPZ for a dedicated private underground fire mains having
> >>>> fire hydrants
> >>>>
> >>>>
> >>>>
> >>>> I am hearing that in Illinois the state plumbing inspectors insist
> >>>> on RPZ back flow prevention for fire hydrants on dedicated
> >>>> underground private service mains. What is up with that?
> >>>>
> >>>> Allan Seidel
> >>>> St. Louis. MO
> >>>> _______________________________________________
> >>>> Sprinklerforum mailing list
> >>>> [email protected]
> >>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>>>
> >>>>
> >>>> -------------- next part -------------- A non-text attachment was
> >>>> scrubbed...
> >>>> Name: winmail.dat
> >>>> Type: application/ms-tnef
> >>>> Size: 4685 bytes
> >>>> Desc: not available
> >>>> URL: <
> >>>> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/
> >>>> att
> >>>> achments/20120605/c0c6b675/attachment.bin
> >>>>>
> >>>> _______________________________________________
> >>>> Sprinklerforum mailing list
> >>>> [email protected]
> >>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>>>
> >>>
> >>>
> >>>
> >>> --
> >>> Ron Greenman
> >>> Instructor
> >>> Fire Protection Engineering Technology Bates Technical College
> >>> 1101 So. Yakima Ave.
> >>> Tacoma, WA 98405
> >>>
> >>> [email protected]
> >>>
> >>> http://www.bates.ctc.edu/fireprotection/
> >>>
> >>> 253.680.7346
> >>> 253.576.9700 (cell)
> >>>
> >>> Member:
> >>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> >>>
> >>> They are happy men whose natures sort with their vocations. -Francis
>
> >>> Bacon, essayist, philosopher, and statesman (1561-1626)
> >>> -------------- next part -------------- An HTML attachment was
> >>> scrubbed...
> >>> URL:
> >>> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/
> >>> att
> >>> achments/20120605/19d8453d/attachment.html>
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>>
> >>
> >>
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL:
> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
> ment
> s/20120606/015d1967/attachment.html>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120607/9c8d00e1/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to