Prior to my arrival, my company designed a group B building with a 300 foot long corridor which had a "slot" atrium. The floor opening consisted of a 3 foot wide slot that ran the entire length along the outside wall. The code consultant recommended a deluge system the entire length of the slot. The architects loved this idea. As a result they will occasionally suggest this as an alternative solution to some scheme they have in their brains at which point I voice loudly how this is the dumbest hair brained idea I had ever seen and the company is very lucky it has not released. Fortunately it was multi-zoned and provided with multiple interlocks.
Jack Fairchild -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bill Brooks Sent: Thursday, June 07, 2012 8:34 AM To: [email protected] Subject: RE: RTI Cloud Deluge Yes we have a rulebook instead of an engineering approach (thank goodness), and yes we have been fumbling around for many years about this cloud thing, but in the name of common sense (which I hope we still have a little of) this design approach must be stopped at all costs. Bill Brooks William N. Brooks, P.E. Brooks Fire Protection Engineering Inc. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Mike Hairfield Sent: Wednesday, June 06, 2012 3:36 PM To: AFSA SprinklerFORUM Subject: RE: RTI You won't believe this! Armstrong ceiling clouds that are arched, architect doesn't want to penetrate the clouds like the Armstrong data sheet shows so we have QR sprinklers above the clouds and a deluge system of sidewall sprinklers feed from the soffits throwing water under the clouds. Some big DA came up with this idea. It's a tiered classroom with a sloping floor, I suggested they install some life preservers for the students so they won't drown when the system trips. Mike > From: [email protected] > To: [email protected] > Subject: RE: RTI > Date: Wed, 6 Jun 2012 19:29:07 +0000 > > Are the detectors at the same temperature as the QR heads? That just > sound weird, what would be in the same room that would be protected by deluge system and also allow QR sprinklers? > > Craig L. Prahl, CET > Fire Protection > CH2MHILL > Lockwood Greene > 1500 International Drive > Spartanburg, SC 29304-0491 > Direct - 864.599.4102 > Fax - 864.599.8439 > CH2MHILL Extension 74102 > [email protected] > > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Mike > Hairfield > Sent: Wednesday, June 06, 2012 2:08 PM > To: AFSA SprinklerFORUM > Subject: RE: RTI > > > There are QR Sprinklers in the same room that has a deluge system with > open heads in it, they want to make sure that the detectors do not > trip the deluge system first. > > > > > > From: [email protected] > > To: [email protected] > > Date: Wed, 6 Jun 2012 12:31:18 -0500 > > Subject: RE: RTI > > > > Curious if you know why the AHJ wanted to know? Listings take care > > of either FR/QR or SR. > > > > Chris Cahill, PE* > > Senior Fire Protection Engineer, Aviation & Facilities Group Burns & > > McDonnell > > 8201 Norman Center Drive > > Bloomington, MN 55437 > > Phone: 952.656.3652 > > Fax: 952.229.2923 > > [email protected] > > www.burnsmcd.com > > > > Proud to be one of FORTUNE's 100 Best Companies to Work For > > *Registered in: MN > > > > > > > > > > -----Original Message----- > > From: [email protected] > > [mailto:[email protected]] On Behalf Of Mike > > Hairfield > > Sent: Wednesday, June 06, 2012 12:26 PM > > To: AFSA SprinklerFORUM > > Subject: RE: RTI > > > > > > Thanks, > > > > They told me it was 36. > > > > Mike > > > > > > > From: [email protected] > > > To: [email protected] > > > Subject: RE: RTI > > > Date: Wed, 6 Jun 2012 17:21:17 +0000 > > > > > > Call Tyco. > > > > > > > > > Craig L. Prahl, CET > > > Fire Protection > > > CH2MHILL > > > Lockwood Greene > > > 1500 International Drive > > > Spartanburg, SC 29304-0491 > > > Direct - 864.599.4102 > > > Fax - 864.599.8439 > > > CH2MHILL Extension 74102 > > > [email protected] > > > > > > > > > > > > -----Original Message----- > > > From: [email protected] > > > [mailto:[email protected]] On Behalf Of > > > Mike Hairfield > > > Sent: Wednesday, June 06, 2012 1:19 PM > > > To: AFSA SprinklerFORUM > > > Subject: RTI > > > > > > > > > I have a AHJ wanting to know what is the RTI for a TYCO FR-B > > > TY3231 155 degree pendent sprinkler. > > > > > > How do I determine the RTI? > > > > > > Mike > > > -------------- next part -------------- An HTML attachment was > > > scrubbed... > > > URL: > > > <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/ > > > atta chments/20120606/0ddfb8a7/attachment.html> > > > _______________________________________________ > > > Sprinklerforum mailing list > > > [email protected] > > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > _______________________________________________ > > > Sprinklerforum mailing list > > > [email protected] > > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > -------------- next part -------------- An HTML attachment was > > scrubbed... > > URL: > > <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/at > > tachments/20120606/47d8575c/attachment.html> > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > -------------- next part -------------- An HTML attachment was > scrubbed... > URL: > <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/atta > chments/20120606/7d67d958/attachment.html> > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment s/20120606/16efcb8d/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum