In our NZ Standard NZS541 a sprinkler with RTI between >50 and <80 is designated a "Special Response Sprinkler". These usually have a 4mm bulb. "Std Response" has a 5mm or larger bulb and the "Fast Response" has a 3mm bulb.
Russell Gregory Ph 03 338 4853 e-mail [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Thursday, 7 June 2012 10:34 PM To: [email protected] Subject: RE:RTI correction, meter, not feet. i should have looked in 13 instead of trying to recall and thinking i needed to convert. but i now have another (perhaps stupid) question re the definition of fast response and standard response: if fast is RTI=50 or less and standard is 80 or more, what is in between called? I am really more interested in the reasoning for the DEFINITION in NFPA #13, not some box of heads in RTI limbo. Any TC members out there not totally fed-up with me yet? _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum