Hello

Well the alarm guys that put the heat detector in the elevator shaft need to 
consider the RTI of the sprinkler head in comparison to the RTI of the Heat 
Detector they put within 24" of the sprinkler head also.  Going to be a Pain 
when the the requirement that anything within 48" of the bottom of the pit 
meets NEMA 4 to coordinate locations of the sprinkler head with the alarm 
device......

Thursday, June 7, 2012, 10:34:32 PM, you wrote:

> In our NZ Standard NZS541 a sprinkler with RTI between >50 and <80 is
> designated a "Special Response Sprinkler". These usually have a 4mm bulb.
> "Std Response" has a 5mm or larger bulb and the "Fast Response" has a 3mm
> bulb.

> Russell Gregory
> Ph  03 338 4853
> e-mail [email protected]


-- 
Best regards,
 Charles                            mailto:[email protected]