Todd,
Simply depends on the construction.  Wood 3' or <, 130 sf; wood > 3', 168
sf; just about everything else, 225 sf.  You can even use EC's.  There is
also the combustible concealed space rule.  These can be used up to 144 sf.

Bob Knight, CET III
208-318-3057
www.firebyknight.com



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Thursday, June 14, 2012 9:05 AM
To: [email protected]
Subject: Drop out ceiling tile area

Is there a restriction on the square footage that can be protected by a
system above a drop-out ceiling? A fire marshal was telling me that there is
a restriction in NFPA 13, but I've never heard of it and can't find it.
Thoughts?