System. Looking if there is any restriction beyond the 52K

At 11:22 AM 6/14/2012, you wrote:
>52,000 sqft is the restriction for any light or ordinary system per level.
>You did say system, not head, correct?
>
>On Thu, Jun 14, 2012 at 8:13 AM, Bob <[email protected]> wrote:
>
>> Todd,
>> Simply depends on the construction.  Wood 3' or <, 130 sf; wood > 3', 168
>> sf; just about everything else, 225 sf.  You can even use EC's.  There is
>> also the combustible concealed space rule.  These can be used up to 144 sf.
>>
>> Bob Knight, CET III
>> 208-318-3057
>> www.firebyknight.com
>>
>>
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Todd
>> Williams
>> Sent: Thursday, June 14, 2012 9:05 AM
>> To: [email protected]
>> Subject: Drop out ceiling tile area
>>
>> Is there a restriction on the square footage that can be protected by a
>> system above a drop-out ceiling? A fire marshal was telling me that there
>> is
>> a restriction in NFPA 13, but I've never heard of it and can't find it.
>> Thoughts?
>>
>> Todd G. Williams, PE
>> Fire Protection Design/Consulting
>> Stonington, CT
>> 860.535.2080
>> www.fpdc.com
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> -----
>> No virus found in this message.
>> Checked by AVG - www.avg.com
>> Version: 2012.0.2180 / Virus Database: 2433/5069 - Release Date: 06/14/12
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>
>
>
>-- 
>Ron Greenman
>Instructor
>Fire Protection Engineering Technology
>Bates Technical College
>1101 So. Yakima Ave.
>Tacoma, WA 98405
>
>[email protected]
>
>http://www.bates.ctc.edu/fireprotection/
>
>253.680.7346
>253.576.9700 (cell)
>
>Member:
>ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>
>They are happy men whose natures sort with their vocations. -Francis Bacon,
>essayist, philosopher, and statesman (1561-1626)
>-------------- next part --------------
>An HTML attachment was scrubbed...
>URL: 
><http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120614/ba1a0509/attachment.html>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to