Not under the circumstances you describe as far as I know.

On Thu, Jun 14, 2012 at 8:34 AM, Todd Williams <[email protected]> wrote:

> System. Looking if there is any restriction beyond the 52K
>
> At 11:22 AM 6/14/2012, you wrote:
> >52,000 sqft is the restriction for any light or ordinary system per level.
> >You did say system, not head, correct?
> >
> >On Thu, Jun 14, 2012 at 8:13 AM, Bob <[email protected]> wrote:
> >
> >> Todd,
> >> Simply depends on the construction.  Wood 3' or <, 130 sf; wood > 3',
> 168
> >> sf; just about everything else, 225 sf.  You can even use EC's.  There
> is
> >> also the combustible concealed space rule.  These can be used up to 144
> sf.
> >>
> >> Bob Knight, CET III
> >> 208-318-3057
> >> www.firebyknight.com
> >>
> >>
> >>
> >> -----Original Message-----
> >> From: [email protected]
> >> [mailto:[email protected]] On Behalf Of Todd
> >> Williams
> >> Sent: Thursday, June 14, 2012 9:05 AM
> >> To: [email protected]
> >> Subject: Drop out ceiling tile area
> >>
> >> Is there a restriction on the square footage that can be protected by a
> >> system above a drop-out ceiling? A fire marshal was telling me that
> there
> >> is
> >> a restriction in NFPA 13, but I've never heard of it and can't find it.
> >> Thoughts?
> >>
> >> Todd G. Williams, PE
> >> Fire Protection Design/Consulting
> >> Stonington, CT
> >> 860.535.2080
> >> www.fpdc.com
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> -----
> >> No virus found in this message.
> >> Checked by AVG - www.avg.com
> >> Version: 2012.0.2180 / Virus Database: 2433/5069 - Release Date:
> 06/14/12
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >
> >
> >
> >--
> >Ron Greenman
> >Instructor
> >Fire Protection Engineering Technology
> >Bates Technical College
> >1101 So. Yakima Ave.
> >Tacoma, WA 98405
> >
> >[email protected]
> >
> >http://www.bates.ctc.edu/fireprotection/
> >
> >253.680.7346
> >253.576.9700 (cell)
> >
> >Member:
> >ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> >
> >They are happy men whose natures sort with their vocations. -Francis
> Bacon,
> >essayist, philosopher, and statesman (1561-1626)
> >-------------- next part --------------
> >An HTML attachment was scrubbed...
> >URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120614/ba1a0509/attachment.html
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120614/f3c591b7/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to