thanks Eric, bathroom in hotel room 13-2007. I have 87 ft2 overall bathroom,
broken up into 3 compartments: 24 ft2 shower enclosure floor to wall, 47 ft2
with a sink, and 16 ft2 with toilet. If the thermal barrier is between a
bathroom and a non bathroom, I think no sprinklers required, as we have the
typical metal stud and gyp walls between these 3 bathrooms and the
non-bathroom spaces.

-----Original Message-----
From: Eric Tysinger [mailto:[email protected]] 
Sent: Friday, August 31, 2012 8:57 AM
To: [email protected]
Subject: RE: thermal barrier

I would assume you are referencing NFPA 13R, 2002 edition. In the 2007
edition the requirement for the thermal barrier has been removed.

2002 edition, section 6.8.2 - thermal barrier required.
2007 edition, section 6.9.2 - not required

Eric Tysinger CET
NICET III - 108988
Project Manager - Fort Myers Branch
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Fort Myers, Florida 33905
p: (239)433-3030 x1240    f: (239)433-3263
C: (239)633-9703

For Fire Alarm Service and Monitoring questions contact us at:
[email protected]

"Ask us how we can eliminate your Fire Alarm phone line bills"
"Ask us about CCTV, Access Control and Security"

Thank you, and have a great day !



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad
Casterline
Sent: Friday, August 31, 2012 9:46 AM
To: [email protected]
Subject: thermal barrier

I searched the archives and found:

 

"The thermal barrier is between the bathroom and the adjacent space".

 

The statement was made by Mr. Craig L. Prahl.

Craig (or any other helpful forumite), is their a code I can reference to
back the statement up?

 

many thanks,

Brad Casterline, NICET IV

Fire Protection Division

 

FSC, Inc.

P: 913-722-3473

[email protected]

www.fsc-inc.com

 

Engineering Solutions for the Built Environment

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120831/7083ea72/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to