The toilet room wall stops 32" short of separating it from the sink room (I
called it an opening in the wall). So there are 3 small bathrooms with 2
non-thermal barriers separating them.
Since the thermal barrier wording mentions ~~including behind shower
enclosures~~, and those are at the wall that separates the bathroom from the
non-bathroom, I am thinking the thermal barrier is NOT required between
bathrooms. I thought if Craig had found his statement in a code I would
start there in perusing an interpretation.   

-----Original Message-----
From: Eric Tysinger [mailto:[email protected]] 
Sent: Friday, August 31, 2012 9:47 AM
To: [email protected]
Subject: RE: thermal barrier

NFPA 13, 2007 does define compartments in 3.3.5. I would think in order to
meet the 55 sqft or less it would be per compartment. With that being the
case I would also think that the thermal barrier would have to be per
compartment as well. I am pretty sure the "full height shower/tub enclosure"
was part of the 1999 edition and has since been removed (as it is not
mentioned in 2002 and 2007). That would mean that you are required to
include the sqft of the tub/shower in the total for the bathroom regardless.
I would say based on your information that the sink/shower room will require
a sprinkler and the toilet room can be omitted, provided you have the
thermal barrier all the way around the toilet room.


Eric Tysinger CET
NICET III - 108988
Project Manager - Fort Myers Branch
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Fort Myers, Florida 33905
p: (239)433-3030 x1240    f: (239)433-3263
C: (239)633-9703

For Fire Alarm Service and Monitoring questions contact us at:
[email protected]

"Ask us how we can eliminate your Fire Alarm phone line bills"
"Ask us about CCTV, Access Control and Security"

Thank you, and have a great day !




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad
Casterline
Sent: Friday, August 31, 2012 10:00 AM
To: [email protected]
Subject: RE: thermal barrier

thanks Eric, bathroom in hotel room 13-2007. I have 87 ft2 overall bathroom,
broken up into 3 compartments: 24 ft2 shower enclosure floor to wall, 47 ft2
with a sink, and 16 ft2 with toilet. If the thermal barrier is between a
bathroom and a non bathroom, I think no sprinklers required, as we have the
typical metal stud and gyp walls between these 3 bathrooms and the
non-bathroom spaces.

-----Original Message-----
From: Eric Tysinger [mailto:[email protected]]
Sent: Friday, August 31, 2012 8:57 AM
To: [email protected]
Subject: RE: thermal barrier

I would assume you are referencing NFPA 13R, 2002 edition. In the 2007
edition the requirement for the thermal barrier has been removed.

2002 edition, section 6.8.2 - thermal barrier required.
2007 edition, section 6.9.2 - not required

Eric Tysinger CET
NICET III - 108988
Project Manager - Fort Myers Branch
Wayne Automatic Fire Sprinklers, Inc.
4683 Laredo Ave.
Fort Myers, Florida 33905
p: (239)433-3030 x1240    f: (239)433-3263
C: (239)633-9703

For Fire Alarm Service and Monitoring questions contact us at:
[email protected]

"Ask us how we can eliminate your Fire Alarm phone line bills"
"Ask us about CCTV, Access Control and Security"

Thank you, and have a great day !



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad
Casterline
Sent: Friday, August 31, 2012 9:46 AM
To: [email protected]
Subject: thermal barrier

I searched the archives and found:

 

"The thermal barrier is between the bathroom and the adjacent space".

 

The statement was made by Mr. Craig L. Prahl.

Craig (or any other helpful forumite), is their a code I can reference to
back the statement up?

 

many thanks,

Brad Casterline, NICET IV

Fire Protection Division

 

FSC, Inc.

P: 913-722-3473

[email protected]

www.fsc-inc.com

 

Engineering Solutions for the Built Environment

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120831/7083ea72/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to