That is because it is in the IBC:

903.4.3 Floor control valves. Approved supervised indicating control valves 
shall be provided at the point of connection to the riser on each floor in 
high-rise buildings.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Dewayne Martinez [mailto:[email protected]] 
Sent: Monday, September 24, 2012 12:49 PM
To: [email protected]
Subject: RE: High rise building - dual floor system supplies?

Thanks,
That's when I have run into it also but someone in the office thought it
was for any high rise so since I couldn't find anything in 13 I thought
I check here just in case.


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Mackinnon
Sent: Monday, September 24, 2012 11:23 AM
To: [email protected]
Subject: RE: High rise building - dual floor system supplies?

The only time I've had to have two water supplies within a high rise,
was a Ritz Carlton (due to a Marriott Hotel Specification) 

Steven MacKinnon
Senior Fire Protection Engineer
Hartcorn Plumbing & Heating Inc.
850 South 2nd Street
Ronkonkoma, NY 11779
631-580-2300 - Office
631-580-1090 - Fax
[email protected]
 
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Monday, September 24, 2012 11:10 AM
To: SprinklerFORUM
Subject: High rise building - dual floor system supplies?

Does a high rise building require that the sprinkler system on each
floor be dual feed?  IE: supplied from 2 individual standpipes per
floor.

Thanks, 

 

Dewayne Martinez

Design Build Fire Protection

262-784-7900 (w)

262-784-8401 (f)

414-349-0468 (cell)

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120924/9381b730/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to