The 2012 IBC requires duel risers when buildings are over 420 feet in height.  
Don't forget the secondary water supply to the fire pump.

[F] 403.3.1 Number of sprinkler risers and system design. Each sprinkler system 
zone in buildings that are more than 420 feet (128 000 mm) in building height 
shall be supplied by no fewer than two risers. Each riser shall supply 
sprinklers on alternate floors. If more than two risers are provided for a 
zone, sprinklers on adjacent floors shall not be supplied from the same riser.

Jack Fairchild

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Dewayne Martinez
Sent: Monday, September 24, 2012 12:49 PM
To: [email protected]
Subject: RE: High rise building - dual floor system supplies?

Thanks,
That's when I have run into it also but someone in the office thought it was 
for any high rise so since I couldn't find anything in 13 I thought I check 
here just in case.


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve Mackinnon
Sent: Monday, September 24, 2012 11:23 AM
To: [email protected]
Subject: RE: High rise building - dual floor system supplies?

The only time I've had to have two water supplies within a high rise, was a 
Ritz Carlton (due to a Marriott Hotel Specification) 

Steven MacKinnon
Senior Fire Protection Engineer
Hartcorn Plumbing & Heating Inc.
850 South 2nd Street
Ronkonkoma, NY 11779
631-580-2300 - Office
631-580-1090 - Fax
[email protected]
 
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne Martinez
Sent: Monday, September 24, 2012 11:10 AM
To: SprinklerFORUM
Subject: High rise building - dual floor system supplies?

Does a high rise building require that the sprinkler system on each floor be 
dual feed?  IE: supplied from 2 individual standpipes per floor.

Thanks, 

 

Dewayne Martinez

Design Build Fire Protection

262-784-7900 (w)

262-784-8401 (f)

414-349-0468 (cell)

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120924/9381b730/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to