That's a good point; the question was whether or not there had to be two
connection on each floor, which is not required. But as you say, for
very tall buildings it is now required that you have two risers
supplying alternate floor.  The code is mute on whether you can connect
a floor to more than one riser, but the implication would be that you
can't unless the adjacent floors can be supplied by a different riser or
risers, which tempers my previous response.

The foregoing is my opinion only and does not necessarily represent the
opinion or intent of the NFPA 14 Technical Committee on Standpipe and
Hose Systems.

Steve Leyton
Protection Design & Consulting
San Diego, CA


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Fairchild, Jack
Sent: Monday, September 24, 2012 9:52 AM
To: [email protected]
Subject: RE: High rise building - dual floor system supplies?

The 2012 IBC requires duel risers when buildings are over 420 feet in
height.  Don't forget the secondary water supply to the fire pump.

[F] 403.3.1 Number of sprinkler risers and system design. Each sprinkler
system zone in buildings that are more than 420 feet (128 000 mm) in
building height shall be supplied by no fewer than two risers. Each
riser shall supply sprinklers on alternate floors. If more than two
risers are provided for a zone, sprinklers on adjacent floors shall not
be supplied from the same riser.

Jack Fairchild

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Monday, September 24, 2012 12:49 PM
To: [email protected]
Subject: RE: High rise building - dual floor system supplies?

Thanks,
That's when I have run into it also but someone in the office thought it
was for any high rise so since I couldn't find anything in 13 I thought
I check here just in case.


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Mackinnon
Sent: Monday, September 24, 2012 11:23 AM
To: [email protected]
Subject: RE: High rise building - dual floor system supplies?

The only time I've had to have two water supplies within a high rise,
was a Ritz Carlton (due to a Marriott Hotel Specification) 

Steven MacKinnon
Senior Fire Protection Engineer
Hartcorn Plumbing & Heating Inc.
850 South 2nd Street
Ronkonkoma, NY 11779
631-580-2300 - Office
631-580-1090 - Fax
[email protected]
 
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Monday, September 24, 2012 11:10 AM
To: SprinklerFORUM
Subject: High rise building - dual floor system supplies?

Does a high rise building require that the sprinkler system on each
floor be dual feed?  IE: supplied from 2 individual standpipes per
floor.

Thanks, 

 

Dewayne Martinez

Design Build Fire Protection

262-784-7900 (w)

262-784-8401 (f)

414-349-0468 (cell)

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120924/9381b730/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to