Chris,

I just think it is unreasonable to rely on the sprinkler contractor to make 
alterations to the construction or tell the GC how to build. What if this was a 
50,000 sqft area, is it protecting life and property at a reasonable cost? I 
know it isn't the Architects fault, I was just poking fun at NFPA for trying to 
be the tail wagging the dog. This isn't a type of storage that has no test 
data, this is a type of construction that I have seen many times yet it defies 
the obstruction rules. Yes it is up to us to design to the type of construction 
not alter the construction to meet one of NFPA's definitions.

No offense taken, I spent many years as a designer and have the requisite thick 
skin.

Ron Fletcher
Aero Phoenix

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Cahill, 
Christopher
Sent: Wednesday, December 19, 2012 7:04 AM
To: [email protected]
Subject: RE: Combustible Concealed Space

There are no NFPA 13 construction requirements.  Yes, there are certain 
non-sprinkler pipe features that must get added when you choose a particular 
sprinkler solution.  It's up to us to design the sprinklers for the building 
design not the other way around.  

In this case fill with insulation is certainly a viable option.  It also sounds 
like there is a ULC vs UL issue.  I would hope an AHJ would consider accepting 
UL, FM, ETL, vDs, BS, EU....or Moe, Larry and Curly Listing services even with 
as implied that is Code prohibited in Canada.  At least read the two testing 
standards of UL and ULC and decide if the difference is material.  And note 
'there is no feasible"  that is a judgment call on what is or is not feasible. 
Implies there is a way but someone doesn't like it.  Remember when putting 
heads under a floating ceiling some considered non-feasible, some probably 
still do.  We all know some think running pipe to EVERY sprinkler head is 
non-feasible because we keep finding glued heads. 

Well what about alternate methods?  If I give the AHJ the CC1 test report 
doesn't that work?  How about covering the side of the truss as if it's a TGI 
and limit volumes to 160 cu.ft.   

So there are 4 potential solutions without pondering very hard:
Insulation
Alternate method - CC1
Sucking it up and doing the non-feasible way Alternate method - make'em TGI like

Can't blame the architect when there are 4 potential solutions.  And even if 
there were none I still don't think you can blame the architect.   

Nothing personal Ron, the above appears harsher than it is meant. 

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in: MN




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, December 18, 2012 1:51 PM
To: [email protected]
Subject: RE: Combustible Concealed Space

It's another case of Architects designing buildings that don't comply with NFPA 
#13s' construction requirements. When will they learn that NFPA 13 is building 
code as well as a sprinkler system installation standard?

Ron Fletcher
Aero Phoenix

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Tuesday, December 18, 2012 11:35 AM
To: [email protected]
Subject: Combustible Concealed Space

I have a combustible concealed space above the main floor of a two storey 
building that is required to be sprinklered. This space is 16" deep and 
consists of open web trusses spaced 16" on-centre. The webs are made of 2x4's, 
causing considerable obstructions. This space qualifies for the use of heads 
listed for this use.

My questions/dilemmas are as following:

(1) There is no feasible possibility to avoid obstructions. Any comments?
(2) As far as I know, the CC heads are only made by TYCO and they are not ULC 
listed. I'm in a Canadian jurisdiction. So can I say there is no listed head 
(as the building code validates only ULC listings) and use standard heads?
(3) If I use CC heads, can I use exposed blazemaster piping (subject to the 
restrictions of course)? The problem is exposed blazemaster piping is allowed 
only in its UL listing and not in ULC. So just going around in circles.

Thanks for any comments.

Tony

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to