Hung from two corners and suspended vertically
Fresh out of a washing machine.


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
g...@rowesprinkler.com



-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams
Sent: Wednesday, January 02, 2013 4:13 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Wet tents drying at 45'

Are the tent wet with water only or are there cleaning solutions involved? Are 
they hung vertically like a shirt or would they be hung by 4 corners, creating 
an obstruction to discharge?


At 03:13 PM 1/2/2013, you wrote:
>Tent drying is a separately walled off area with insulated panels and 
>temperature control. I'm assuming there will be some supports below the BA 
>Fans (20' circumference) so there's something to hang the tents from.
>
>
>George L.  Church, Jr., CET  
>Rowe Sprinkler Systems, Inc.
>PO Box 407, Middleburg, PA 17842
>877-324-ROWE       570-837-6335 fax
>g...@rowesprinkler.com
>
>
>-----Original Message-----
>From: sprinklerforum-boun...@firesprinkler.org 
>[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Tom Duross
>Sent: Monday, December 31, 2012 7:25 PM
>To: sprinklerforum@firesprinkler.org
>Subject: RE: Wet tents drying at 45'
>
>Open floor plan?
>
>-----Original Message-----
>From: sprinklerforum-boun...@firesprinkler.org
>[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
>Sent: Monday, December 31, 2012 3:21 PM
>To: sprinklerforum@firesprinkler.org
>Subject: Re: Wet tents drying at 45'
>
>Ok. 2007 #13, steel joist noncombustible construction, and qualify someone has 
>BA Fan interlock off WFS. 
>Glc
>
>Sent from my iPhone
>
>On Dec 31, 2012, at 3:17 PM, "George Church" <g...@rowesprinkler.com> wrote:
>
>> Here's an unusual one. Tent rental firm, they have a 45' high bay with 
>> BA
>Fans and floor heat and a couple Unit heaters. They hoist them with wires and 
>spread them out. Separate high piled rack storage outside this area, so fuel 
>load is just what is hanging. Fire resistant canvass primarily, plus the fun 
>of the window panels being a non expanded plastic. 
>> Any ideas?
>> Glc
>> Rowe Sprinkler
>> 
>> Sent from my iPhone
>> 
>> On Dec 28, 2012, at 10:15 PM, "Ron Greenman" <rongreen...@gmail.com>
>wrote:
>> 
>>> Well, a flow switch is hardly an alarm check valve. if it will deform 
>>> in forward flow it will deform in backward flow. It canot therefore 
>>> be a check or one-way valve as it can't "check" flow in either direction.
>>> 
>>> On Fri, Dec 28, 2012 at 3:52 PM, Sprinkler Academy - C Bilbo < 
>>> prodesigngr...@msn.com> wrote:
>>> 
>>>> 
>>>> Dude! Show him the pictures in Figure A.8.16.1.1 (2007 edition, 
>>>> similar in
>>>> 2010) It shows above the Alarm Check and the control valve. But then 
>>>> it also shows BELOW the Alarm Check and BELOW the DPV on a manifold.
>>>> You show it "AFTER" a check and "Under" the Alarm valve "just like 
>>>> the pictures in NFPA 13"!!!! Congrats, you win.
>>>> 
>>>> It should be recognized that the above is my opinion as a member of 
>>>> the NFPA, and has not been processed as a formal interpretation in 
>>>> accordance with the NFPA Regulations Governing Committee Projects 
>>>> and should therefore not be considered, nor relied upon, as the 
>>>> official position of the the NFPA, nor any of their technical
>committees.
>>>> 
>>>> Sincerely,
>>>> 
>>>> 
>>>> Cecil Bilbo
>>>> Academy of Fire Sprinkler Technology Champaign, IL
>>>> 217.607.0325
>>>> www.sprinkleracademy.com
>>>> 
>>>> ce...@sprinkleracademy.com
>>>> 
>>>> 
>>>> 
>>>> OUR STUDENTS SAVE LIVES!!
>>>> 
>>>> 
>>>>> Date: Fri, 28 Dec 2012 13:57:21 -0500
>>>>> To: sprinklerforum@firesprinkler.org
>>>>> From: t...@fpdc.com
>>>>> Subject: RE: FDC location with riser manifold
>>>>> 
>>>>> That has basically been my argument. However, how do I convince him 
>>>>> that
>>>> a riser manifold is not an alarm valve?
>>>>> 
>>>>> 
>>>>> At 12:59 PM 12/28/2012, you wrote:
>>>>>> 2013 edition
>>>>>> 8.16.1.1.3.2    A listed backflow prevention device shall be
>considered
>>>> a check valve, and an additional check valve shall not be required.
>>>>>> 
>>>>>> Your FDC is on the system side of the backflow/check valve.
>>>>>> 
>>>>>> Duane Johnson, PE
>>>>>> Program Manager
>>>>>> Division of the Fire Marshal (Contractor) Office of Research 
>>>>>> Services National Institutes of Health
>>>>>> 301-496-0487
>>>>>> 
>>>>>> "Protecting Science - One Sprinkler at a Time"
>>>>>> 
>>>>>> 
>>>>>> -----Original Message-----
>>>>>> From: Todd Williams [mailto:t...@fpdc.com]
>>>>>> Sent: Friday, December 28, 2012 12:32 PM
>>>>>> To: sprinklerforum@firesprinkler.org
>>>>>> Subject: FDC location with riser manifold
>>>>>> 
>>>>>> I had an AHJ come back with a comment regarding a location of an 
>>>>>> FDC on
>>>> a system I designed. The system has a single riser. The water main 
>>>> comes into the building approximately 1'-6" AFF. An elbow is 
>>>> installed and the backflow preventer is running horizontally 
>>>> parallel to
>the outside wall.
>>>> The main turns vertical after the BFP and rises up at a riser 
>>>> manifold (not
>>>> check) and on to the system. After the BFP, I called for a Tee with 
>>>> one outlet looking up and the other horizontal to the check and FDC.
>>>> For design reasons, this has a significant advantage. The AHJ's 
>>>> contention is that the BFP needs to be taken off above the manifold 
>>>> because "that is what is says in NFPA 13". Section 8.16.2.4.2 (1) 
>>>> states it shall be installed "on the system side of the system 
>>>> control, check and alarm valves." His contention is that it says a 
>>>> riser manifold is an alarm valve, which requires the FDC to be taken 
>>>> off above. My contention is that since it is not a check valve, then 
>>>> it doesn't make a d
>>>>> i
>>>>>> fference if it is above or below. The AHJ is an NFPA 13
>>>> fundamentalist and if it is not in there, it isn't the truth. Thoughts?
>>>>>> 
>>>>>> Todd G. Williams, PE
>>>>>> Fire Protection Design/Consulting
>>>>>> Stonington, CT
>>>>>> 860.535.2080
>>>>>> www.fpdc.com
>>>>>> 
>>>>>> _______________________________________________
>>>>>> Sprinklerforum mailing list
>>>>>> Sprinklerforum@firesprinkler.org
>>>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>>> _______________________________________________
>>>>>> Sprinklerforum mailing list
>>>>>> Sprinklerforum@firesprinkler.org
>>>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>> 
>>>>> Todd G. Williams, PE
>>>>> Fire Protection Design/Consulting
>>>>> Stonington, CT
>>>>> 860.535.2080
>>>>> www.fpdc.com
>>>>> 
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> Sprinklerforum@firesprinkler.org
>>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>> 
>>>> -------------- next part -------------- An HTML attachment was 
>>>> scrubbed...
>>>> URL: <
>>>> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/att
>>>> achments/20121228/9e009fd0/attachment.html
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> Sprinklerforum@firesprinkler.org
>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>> 
>>> 
>>> 
>>> --
>>> Ron Greenman
>>> Instructor
>>> Fire Protection Engineering Technology Bates Technical College
>>> 1101 So. Yakima Ave.
>>> Tacoma, WA 98405
>>> 
>>> rgreen...@bates.ctc.edu
>>> 
>>> http://www.bates.ctc.edu/fireprotection/
>>> 
>>> 253.680.7346
>>> 253.576.9700 (cell)
>>> 
>>> Member:
>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>>> 
>>> They are happy men whose natures sort with their vocations. -Francis 
>>> Bacon, essayist, philosopher, and statesman (1561-1626)
>>> -------------- next part -------------- An HTML attachment was 
>>> scrubbed...
>>> URL: 
>>> <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/att>> 
>>> achments/20121228/8e0b970a/attachment.html>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> Sprinklerforum@firesprinkler.org
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> _______________________________________________
>> Sprinklerforum mailing list
>> Sprinklerforum@firesprinkler.org
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>_______________________________________________
>Sprinklerforum mailing list
>Sprinklerforum@firesprinkler.org
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>_______________________________________________
>Sprinklerforum mailing list
>Sprinklerforum@firesprinkler.org
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>_______________________________________________
>Sprinklerforum mailing list
>Sprinklerforum@firesprinkler.org
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to