Bobby:

In a pinch, FM and NFPA typically recommends 0.3 gpm / ft sq. A.S. over
many combustible liquids. Since it is confined to a small pit, I would be *more
than comfortable *with this application rate of water-only agent.  This
applicaton will  not put our fire out, but it will keep things cool till
foam or dry-chem puts the kabosh on it.

Be sure to interface with the GC about drainage.  If none, fine.  If there
is drainage, have a P-trap in the drain so fire doesn't pass down and
continue the same.

(2008 NFPA 30 Table 16.5.2.1)


scot deal
Excelsior Fire/Risk Engineering