Thank you, Scot. For worse case scenario purposes, I applied .40 using the K-11.2 per Table 23.7 and calc'ed it along with my inside RA to be sure it would work for pricing purposes. It calc'd just fine since the engineer is requiring a max. water flow velocity of 20fps. Had to tweak my mains just a bit to lower my velocity but it works.
Can anyone guess what my first question will be to the engineer in the Pre-bid Meeting next week? Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell www.keyfireprotection.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of å... .... Sent: Friday, January 25, 2013 10:51 AM To: [email protected] Subject: Exposure Protection for Walls Bobby: In a pinch, FM and NFPA typically recommends 0.3 gpm / ft sq. A.S. over many combustible liquids. Since it is confined to a small pit, I would be *more than comfortable *with this application rate of water-only agent. This applicaton will not put our fire out, but it will keep things cool till foam or dry-chem puts the kabosh on it. Be sure to interface with the GC about drainage. If none, fine. If there is drainage, have a P-trap in the drain so fire doesn't pass down and continue the same. (2008 NFPA 30 Table 16.5.2.1) scot deal Excelsior Fire/Risk Engineering -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment s/20130125/3bf7e5a1/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum ----- No virus found in this message. Checked by AVG - www.avg.com Version: 2013.0.2890 / Virus Database: 2639/6055 - Release Date: 01/24/13 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum