MOU is Memorandum of Understanding.   Meaning his jurisdiction has a
deal with the SFM ceding local authority to his agency.   His
mischaracterizing it though, to say that it means he can do whatever he
wants.   The code section he refers to is sarcastically called "The God
Clause", as many fire officials believe it's all-empowering.   In CA,
the operating relationship between LFA's and the SFM is that and LFA is
charged with enforcing state code, but can exceed that when there is a
compelling situation or condition, and they can amend state code through
a process that involves ordinance and filing a white paper with the
OSFM.    Under our current SFM, I find that our state is working very,
very well in that regard and when a local wants or needs something above
and beyond, they generally require it in a lucid, substantiated and
documented manner.


Steve Leyton




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, January 30, 2013 8:29 AM
To: [email protected]
Subject: RE: Fire Marshal requirement?

Hehe, I like that. "I told them that if we were the EOR then we would
have appreciated the opportunity to develop the bid docs and collect the
fee..." I may use that in the future if that's okay?

Ron Fletcher
Aero Phoneix

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Rod
DiBona
Sent: Wednesday, January 30, 2013 9:17 AM
To: [email protected]
Subject: RE: Fire Marshal requirement?

Well I don't blame you for venting. This is becoming more and more
common. It is simply not right. I have a similar situation with regards
to who is the EOR. They do the life safety report, drawings and
specifications that we are tied to and that bears their stamp. When the
rubber meets the road they claim we are the design build contractor. I
like our chances in arbitration but is it worth it? Sometimes you lose
even when you win. I told them that if we were the EOR then we would
have appreciated the opportunity to develop the bid docs and collect the
fee....No response...

Rod at Rapid

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, January 30, 2013 6:17 AM
To: [email protected]
Subject: RE: Fire Marshal requirement?

The following are parts of the FM's response to my email pointing out
the code language. Names and places are left out so I don't get more
trouble than I'm already in.

"Stop!  This is not a debate nor will this discussion continue." ...  "I
do not have time, nor does my staff to go back and forth with you on
this and it will hold up the project." Is he threatening to hold up the
project? "By MOU (what is MOU?) with the State Fire Marshal, I am the
only authority for fire code for blah blah balh. Read Section 104.1,
104.8 and many other sections ...it is my authority to enforce,
interpret, and approve modifications of alternative methods to meet the
intent, or increase the minimum code requirements."  

I love the sprinkler business. Where else can we lowly contractors come
in contact with such powerful and influential leaders? (lol)

Needless to say we are installing the SP system shown on the contract
drawings even though it doesn't meet code. We were also informed by the
consultant that did the drawings (a nationally known FP firm) that their
drawings were to show possible pipe routing for space allocation with
other trades and are not to be interpreted as installation drawings.
They also pointed out the we, Aero, are the EOR not them. Even though
they did a life safety report and 4 or 5 FP plans for the project with a
PE stamp.

I'm probably going to get hand slapped for this but I needed to vent.

Ron Fletcher
Aero Phoenix


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bruce
Verhei
Sent: Tuesday, January 29, 2013 6:30 PM
To: [email protected]
Subject: RE: Fire Marshal requirement?

Note comment is to million sf, not small building being discussed. 

Have you had discussion with architect. They should be familiar with any
site specific items done as trade offs.

It is rather uncommon for these to be included in bid requests.

Bv

Bv

-----Original message-----
From: [email protected]
To: [email protected]
Sent: Tue, Jan 29, 2013 21:03:41 GMT+00:00
Subject: RE: Fire Marshal requirement?

We have done a few million plus sqft. one story buildings (distribution
center). The biggest issue usually is the 250' verses 400' exit travel
and smoke vents with ESFR's. No standpipes required.

Ron Fletcher
Aero Phoneix 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Fairchild, Jack
Sent: Tuesday, January 29, 2013 11:17 AM
To: [email protected]
Subject: RE: Fire Marshal requirement?

Looks like 905.4 remains relatively unchanged in 2012, but there is zero
reference as to when to apply it.

What about a million sq.ft. single story building?

Jack Fairchild


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Johnson,
Duane (NIH/OD/ORS) [C]
Sent: Tuesday, January 29, 2013 12:58 PM
To: '[email protected]'
Subject: RE: Fire Marshal requirement?

Interesting interpretation.

FYI, the 2012 edition removed "and in the locations indicated in
Section905.4, 905.5, and 905.6".

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor) Office of Research Services
National Institutes of Health
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Fairchild, Jack [mailto:[email protected]]
Sent: Tuesday, January 29, 2013 12:44 PM
To: [email protected]
Subject: RE: Fire Marshal requirement?

2009 IFC 905.3 read strictly does not tie standpipe hose connections to
height.  It states ..."where required by sections 905.3.1 through
905.3.7  
and in the locations indicated in Sections 905.4, 905.5, and 905.6."   
Section 905.4 needs to be applied regardless of 905.3.1 because of the
"and"  
after 905.3.1 in section 905.3.  (wow that's wordy).

Personally I do not believe the intent is to provide hose connections in
any building that has more than one floor or where the fire truck is
more than
200 feet from any point in the building, but I see how it could be read
that way.  I always thought 905.4 was intended for very expansive
buildings such as those seen out west.  Maybe this section should be
tied to a square footage.

Jack Fairchild


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Johnson,
Duane (NIH/OD/ORS) [C]
Sent: Tuesday, January 29, 2013 12:21 PM
To: '[email protected]'
Subject: RE: Fire Marshal requirement?

Per IBC:

905.3.1  Class III standpipe systems shall be installed throughout
buildings where the floor level of the highest story is located more
than 30 feet
(9144 mm) above the lowest level of fire department vehicle access, or
where the floor level of the lowest story is located more than 30 feet
(9144 mm) below the highest level of fire department vehicle access.

STORY. That portion of a building included between the upper surface of
a floor and the upper surface of the floor or roof next above (also see
"Basement," "Building height," "Grade plane" and "Mezzanine"). It is
measured as the vertical distance from top to top of two successive
tiers of beams or finished floor surfaces and, for the topmost story,
from the top of the floor finish to the top of the ceiling joists or,
where there is not a ceiling, to the top of the roof rafters.

MEZZANINE. An intermediate level or levels between the floor and ceiling
of any story and in accordance with Section 505.

505.2 Mezzanines.
A mezzanine or mezzanines in compliance with Section 505.2 shall be
considered a portion of the story below.

A 32' high mezzanine doesn't constitute standpipes.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor) Office of Research Services
National Institutes of Health
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: [email protected] [mailto:[email protected]]
Sent: Tuesday, January 29, 2013 11:59 AM
To: [email protected]
Subject: RE: Fire Marshal requirement?

A small 2 story area the rest is all one story. There is a running track
on a mezzanine that circles the gym that is at 32 ft. high but it is
open to the gym. This is an addition to a building that is sprinklered
but without standpipes. The new addition meets all the exiting and
egress requirements so that is not an issue.

Ron Fletcher
Aero Phoenix

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Leyton
Sent: Tuesday, January 29, 2013 9:36 AM
To: [email protected]
Subject: RE: Fire Marshal requirement?

How many stories is the building, and on what floor is this condition?


Steve Leyton



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, January 29, 2013 7:16 AM
To: [email protected]
Subject: Fire Marshal requirement?

This from a Fire Marshal for a large University in AZ. We were having
trouble locating hose valves in the one story area of the building.
There are only two stairs in the building and they are more than 200 ft.
from parts of the gymnasium. We reviewed the code and offered a credit
to delete the standpipe system because we didn't think it was required.
This the response from the FM. He wants all interior points to be with
150 feet from where they park a fire truck.

"If you send a too scale plan from where fire trucks will be at all
points of entry to the building and can show that nothing is more than
150' I will entertain the suggestion of no standpipes.  I have seen
everything that
****** has been shown and it is not represented well.
This includes the existing building since the existing building had
adequate coverage and did not need a standpipe before the add-on.  Now
that there is an add-on where there is no access at the center point it
affects both the new and old and we need assurance with a too scale
drawing from fire truck to all areas of all floors.  Discussing it does
not solve anything until you can also prove it on paper too scale "as
the hose lays and not the crow flys."

I have difficulty finding a way to talk to someone like this. 

Ron Fletcher
Aero Phoenix

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20130129/5bfb9af8/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to