> Agree with you.  No check valves required.
>
> Fire sprinklers save lives
>
> Sent from my iPad
>
> On May 1, 2013, at 9:44 PM, "Charles Thurston" <[email protected]> wrote:
>
> > Hello Greg,
> >
> > Is it a "Manual Dry" system?  If so we do not and the AHJs in the area
> see no reason to.
> >
> > Wednesday, May 1, 2013, 9:38:18 PM, you wrote:
> >
> >> Are you required to put check valves on FDC's supplyign dry standpipe
> >> systems such as on docks etc?
> >
> >> Thanks,
> >
> >
> >
> >
> >
> > --