While back feeding is true they wouldn't take the hose off until they bled down 
the hose.  Each connection off a fire truck has a bleed valve.  With no check 
they'll just need to bleed the hose and volume of the standpipe.  I don't see 
the big deal either way.  I didn't read the Code though so don't take that as 
analysis one is needed or not. 

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation & Facilities Group
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bobby 
Gillett
Sent: Thursday, May 02, 2013 7:54 AM
To: [email protected]
Subject: RE: check valves on dry standpipes

My only thought is when the fire department disconnects their hoses the water 
can come back through the FDC - some people may still install single clapper 
FDC's not thinking ahead or the clappers could stick or malfunction as well. 

Greg - in your case I could understand not needing one, other than the fact it 
is required. I would check with the AHJ and see if they will agree with you, 
then you are covered. 

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax
(731) 267-4853 cell
www.keyfireprotection.com
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John
Denhardt
Sent: Thursday, May 02, 2013 7:40 AM
To: [email protected]
Subject: RE: check valves on dry standpipes

That is very interesting.  I wonder what is the reason one is required?

Steve?????

John August Denhardt, P.E., FSFPE
Strickland Fire Protection Incorporated
5113 Berwyn Road
College Park, Maryland 20740
Office Telephone Number:  301-474-1136
Mobile Telephone Number:  301-343-1457
FIRE SPRINKLERS SAVE LIVES - Can you live without them?


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bobby
Gillett
Sent: Thursday, May 02, 2013 7:07 AM
To: [email protected]
Subject: RE: check valves on dry standpipes

We did a manual dry in a parking garage a few years ago, I asked this
question to the local AHJ and he did require one. NFPA 14 (2013) - 6.4.2
requires one.

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax 
(731) 267-4853 cell
www.keyfireprotection.com
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Greg
McGahan
Sent: Wednesday, May 01, 2013 10:01 PM
To: [email protected]
Subject: Re: check valves on dry standpipes

T
hanks - that makes three!~!


On Wed, May 1, 2013 at 8:45 PM, John Denhardt
<[email protected]>wrote:

> Agree with you.  No check valves required.
>
> Fire sprinklers save lives
>
> Sent from my iPad
>
> On May 1, 2013, at 9:44 PM, "Charles Thurston" <[email protected]> wrote:
>
> > Hello Greg,
> >
> > Is it a "Manual Dry" system?  If so we do not and the AHJs in the area
> see no reason to.
> >
> > Wednesday, May 1, 2013, 9:38:18 PM, you wrote:
> >
> >> Are you required to put check valves on FDC's supplyign dry standpipe
> >> systems such as on docks etc?
> >
> >> Thanks,
> >
> >
> >
> >
> >
> > --
> > Best regards,
> > Charles                            mailto:[email protected]
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2013.0.3272 / Virus Database: 3162/6290 - Release Date: 05/01/13

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2013.0.3272 / Virus Database: 3162/6290 - Release Date: 05/01/13

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to