Draining system is one use of outlet at ground floor, usually only a few feet 
above FDC level. If you are in a location where water matters, it is even a 
recruit academy drill to hook up to lowest outlet and drain to desired 
location. 
Then with only a few feet of head push against the FDC opening clappers is not 
a problem for either water quantity or force. Lets say 8' x 0.433 psi /ft x 4.9 
sq. in ~= 17 pounds + spring. 

Might be the reason designers and reviewers sometimes see need for lowest 2 
1/2" outlet differently. 

bv 


----- Original Message -----
From: "Bobby Gillett" <[email protected]> 
To: [email protected] 
Sent: Thursday, May 2, 2013 5:54:24 AM 
Subject: RE: check valves on dry standpipes 

My only thought is when the fire department disconnects their hoses the 
water can come back through the FDC - some people may still install single 
clapper FDC's not thinking ahead or the clappers could stick or malfunction 
as well. 

Greg - in your case I could understand not needing one, other than the fact 
it is required. I would check with the AHJ and see if they will agree with 
you, then you are covered. 

Bobby Gillett 
Sr. Project Manager 
Key Fire Protection, Inc. 
(731) 424-0130 office (731) 424-9285 fax 
(731) 267-4853 cell 
www.keyfireprotection.com 


-----Original Message----- 
From: [email protected] 
[mailto:[email protected]] On Behalf Of John 
Denhardt 
Sent: Thursday, May 02, 2013 7:40 AM 
To: [email protected] 
Subject: RE: check valves on dry standpipes 

That is very interesting. I wonder what is the reason one is required? 

Steve????? 

John August Denhardt, P.E., FSFPE 
Strickland Fire Protection Incorporated 
5113 Berwyn Road 
College Park, Maryland 20740 
Office Telephone Number: 301-474-1136 
Mobile Telephone Number: 301-343-1457 
FIRE SPRINKLERS SAVE LIVES - Can you live without them? 


-----Original Message----- 
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bobby 
Gillett 
Sent: Thursday, May 02, 2013 7:07 AM 
To: [email protected] 
Subject: RE: check valves on dry standpipes 

We did a manual dry in a parking garage a few years ago, I asked this 
question to the local AHJ and he did require one. NFPA 14 (2013) - 6.4.2 
requires one. 

Bobby Gillett 
Sr. Project Manager 
Key Fire Protection, Inc. 
(731) 424-0130 office (731) 424-9285 fax 
(731) 267-4853 cell 
www.keyfireprotection.com 

-----Original Message----- 
From: [email protected] 
[mailto:[email protected]] On Behalf Of Greg 
McGahan 
Sent: Wednesday, May 01, 2013 10:01 PM 
To: [email protected] 
Subject: Re: check valves on dry standpipes 

T 
hanks - that makes three!~! 


On Wed, May 1, 2013 at 8:45 PM, John Denhardt 
<[email protected]>wrote: 

> Agree with you. No check valves required. 
> 
> Fire sprinklers save lives 
> 
> Sent from my iPad 
> 
> On May 1, 2013, at 9:44 PM, "Charles Thurston" <[email protected]> wrote: 
> 
> > Hello Greg, 
> > 
> > Is it a "Manual Dry" system? If so we do not and the AHJs in the area 
> see no reason to. 
> > 
> > Wednesday, May 1, 2013, 9:38:18 PM, you wrote: 
> > 
> >> Are you required to put check valves on FDC's supplyign dry standpipe 
> >> systems such as on docks etc? 
> > 
> >> Thanks, 
> > 
> > 
> > 
> > 
> > 
> > -- 
> > Best regards, 
> > Charles mailto:[email protected] 
> > 
> > _______________________________________________ 
> > Sprinklerforum mailing list 
> > [email protected] 
> > 
> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
> _______________________________________________ 
> Sprinklerforum mailing list 
> [email protected] 
> 
> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
> 



-- 
Greg McGahan 
Living Water Fire Protection, LLC <http://www.livingwaterfp.com> 
1160 McKenzie Road 
Cantonment, FL 32533 
850-937-1850 
fax 850-937-1852 
_______________________________________________ 
Sprinklerforum mailing list 
[email protected] 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 

----- 
No virus found in this message. 
Checked by AVG - www.avg.com 
Version: 2013.0.3272 / Virus Database: 3162/6290 - Release Date: 05/01/13 

_______________________________________________ 
Sprinklerforum mailing list 
[email protected] 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
_______________________________________________ 
Sprinklerforum mailing list 
[email protected] 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 

----- 
No virus found in this message. 
Checked by AVG - www.avg.com 
Version: 2013.0.3272 / Virus Database: 3162/6290 - Release Date: 05/01/13 

_______________________________________________ 
Sprinklerforum mailing list 
[email protected] 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to