Section 8.6.4.1.2(5) allows the sprinkler deflector to be above the bottom
of the tees providing the deflectors comply with Table 8.6.5.1.2.  That
still may not get you 7'-0" clear, but it's closer.

Ed Kramer
Lawrence, KS

> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Jay
> White
> Sent: Wednesday, May 08, 2013 8:04 AM
> To: [email protected]
> Subject: Sprinkler Design Of Parking Garage
> 
> The IBC Code says you have to have 7’0” clearance in a parking garage.
> We are having elevation clearance problems with our sprinkler pipe. Does
> anyone know of a exception to the code that allows you to be below 7’-
> 0”? Concrete tee construction. Bottom of the tee is 7’-3 ¼”.  Deflector
> has to maintain a 1” mninimum from bottom of tee. Dry system installed.
> Any help would be appreciated.
> 
> 
> 