Hello, NFPA 13 quoted at bottom w/ the relevant code section:

With the 15 ft. extending into the lesser hazard is the intention to make this 
extended area part of the hydraulic design area (to be included in calcs) or 
simply to extend the results of the calculations into this area? My impression 
is the latter but I would like to see if people concur with that.

Thanks,
RB





NFPA 13: 2007

11.1.2

(1)     Where areas are not physically separated by a barrier or partition 
capable of delaying heat from a fire in one area from fusing sprinklers in the 
adjacent area, the required sprinkler protection for the more demanding design 
basis shall extend 15 ft (4.6 m) beyond its perimeter. 