If there's a question cal. It both ways. Most demanding wins. Rinse and repeat 
design if the more demanding doesn't jive with the supply. Call it a day and 
hit the bars if you're good.

Sent from my iPhone

On May 8, 2013, at 11:14 AM, Ralphy Henderson <[email protected]> wrote:

> Hello, NFPA 13 quoted at bottom w/ the relevant code section:
> 
> With the 15 ft. extending into the lesser hazard is the intention to make 
> this extended area part of the hydraulic design area (to be included in 
> calcs) or simply to extend the results of the calculations into this area? My 
> impression is the latter but I would like to see if people concur with that.
> 
> Thanks,
> RB
> 
> 
> 
> 
> 
> NFPA 13: 2007
> 
> 11.1.2
> 
> (1)     Where areas are not physically separated by a barrier or partition 
> capable of delaying heat from a fire in one area from fusing sprinklers in 
> the adjacent area, the required sprinkler protection for the more demanding 
> design basis shall extend 15 ft (4.6 m) beyond its perimeter. 