I am working on a building that has a static pressure of 80 PSI and a residual pressure of 50 PSI. The building has a fire pump rated at 750 gal 70 psi.
The questions was raised about the maximum arm over length for sprinklers on the 6th floor of the project that is 93' high to the head location. Do I determine the working pressure from the static or residual pressure when determining if the working pressure is over the 100 PSI requirement to require hangers at a maximum of 12" Thanks in advance for any comments -- Craig Leadbetter Safeguard of Marquette PO Box 116 Marquette, MI 49855 (O) 906-475-9955 (F) 906-475-5474 (C) 906-362-5393 [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org